The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 137 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#212283 - 12/28/13 11:13 AM Bonding temporary modular equipment installations
LarryC Offline

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
Building industrial equipment that is installed outside. These systems are modular in nature and can be or will be moved from one location to another.
General set up is a central power entry module, that then feeds one to six sub systems. Power for each subsystem is plugged in via a suitable cord and weather tight connector.
Total system power is between 10 and 50 KVA at 3 phase 240 depending on system configuration.

Bonding will probably be separate suitably sized conductor(s) tying all of the structures together.

My question is: What would be a suitable method of testing the bonding to verify everything has a nice low impedance path back to the PE terminal?

I believe I need approximately 200 A AC or DC for 1 minute to perform this verification test.

My thoughts are a constant current power supply like a stick arc welder or perhaps a 1 KW 12/24 buck/boost transformer and a large variac.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#212286 - 12/28/13 07:53 PM Re: Bonding temporary modular equipment installations [Re: LarryC]
Scott35 Offline

Broom Pusher and

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA

One test may be done using an array of Fixed Resistance Heater Elements connected to the far end of each Circuit, then measure the Voltage at each end to determine the Voltage Loss.
Apply the Volt Drop (E-loss) against the drawn Amperes (I) to achieve the Conductor Impedance (Z).

--Scott (EE)