#211878 - 11/19/13 08:15 PM Common EGC for circuits in PVC raceway
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Can I use the same EGC for running a 20a 120v.circuit and a 20a 277v. circuit in a PVC raceway? Code reference please if available.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#211881 - 11/19/13 10:26 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1309
Loc: Alaska
Yup
_________________________
"Live Awesome!" - Kevin Carosa
Top
#211884 - 11/19/13 11:50 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
If they are coming from the same service I think a single #12 would do it. 250.122(C)
_________________________
Greg Fretwell
Top
#211886 - 11/20/13 09:47 AM Re: Common EGC for circuits in PVC raceway [Re: George Little]
twh Offline
Member
Registered: 03/11/04
Posts: 899
Loc: Regina, Sask.
Can you run circuits from two different panels in the same conduit?
Top
#211888 - 11/20/13 12:13 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
Up to 600v you can combine circuits of different systems in the same raceway provided they are all insulated for the highest voltage-- 300.3(C).

Since a metal raceway would be allowed as the EGC for the 120v and 277v circuits, and I find no language that prohibits it, a single conductor EGC would be allowable as well. Circuitwise, the pipe and conductor work the same way.
Top
#211890 - 11/20/13 03:34 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
The issue seems to be, if you are coming out of two different panels, which you would be, is it proper or necessary to make a three wire splice of the ECG at the common J-box and run a separate wire from there to each panel. I say yes.


300.3(b)
_________________________
George Little
Top
#211891 - 11/20/13 04:09 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
George:
It sounds like you have a EGC with each circuit, going to the j-box, correct?

Then, IMHO, all the EGCs should be spliced together at that point.
_________________________
John
Top
#211892 - 11/20/13 04:11 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
That's correct John, and I believe that the way it should be.
_________________________
George Little
Top
#211898 - 11/20/13 06:13 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
Steve T Offline
Member
Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
If you had a metal raceway, that's the way it would be too, so I had imagined it the same way you are describing. If you ran separate EGCs for the whole run, you'd still have to bond them to the metal boxes, so they would be bonded together at that common point anyways.
Top
#211917 - 11/22/13 08:26 PM Re: Common EGC for circuits in PVC raceway [Re: HotLine1]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1309
Loc: Alaska
One grounding conductor per conduit sized for the largest circuit within the conduit Doesn't matter if its six different systems in it. Only exeception is isolated grounding. In a ground fault in a properly grounded system the fault will go back to the panel with that supplied the fault. Each service if grounded properly is bonded together for zero potential. So no one becomes a bonding jumper themselves
_________________________
"Live Awesome!" - Kevin Carosa
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals