The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
1 registered (ampherder), 63 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#211878 - 11/19/13 08:15 PM Common EGC for circuits in PVC raceway
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Can I use the same EGC for running a 20a 120v.circuit and a 20a 277v. circuit in a PVC raceway? Code reference please if available.
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#211881 - 11/19/13 10:26 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
Yup
_________________________
"Live Awesome!" - Kevin Carosa

Top
#211884 - 11/19/13 11:50 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
If they are coming from the same service I think a single #12 would do it. 250.122(C)
_________________________
Greg Fretwell

Top
#211886 - 11/20/13 09:47 AM Re: Common EGC for circuits in PVC raceway [Re: George Little]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Can you run circuits from two different panels in the same conduit?

Top
#211888 - 11/20/13 12:13 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
Steve T Offline
Member

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
Up to 600v you can combine circuits of different systems in the same raceway provided they are all insulated for the highest voltage-- 300.3(C).

Since a metal raceway would be allowed as the EGC for the 120v and 277v circuits, and I find no language that prohibits it, a single conductor EGC would be allowable as well. Circuitwise, the pipe and conductor work the same way.

Top
#211890 - 11/20/13 03:34 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
The issue seems to be, if you are coming out of two different panels, which you would be, is it proper or necessary to make a three wire splice of the ECG at the common J-box and run a separate wire from there to each panel. I say yes.


300.3(b)
_________________________
George Little

Top
#211891 - 11/20/13 04:09 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
George:
It sounds like you have a EGC with each circuit, going to the j-box, correct?

Then, IMHO, all the EGCs should be spliced together at that point.
_________________________
John

Top
#211892 - 11/20/13 04:11 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
That's correct John, and I believe that the way it should be.
_________________________
George Little

Top
#211898 - 11/20/13 06:13 PM Re: Common EGC for circuits in PVC raceway [Re: George Little]
Steve T Offline
Member

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
If you had a metal raceway, that's the way it would be too, so I had imagined it the same way you are describing. If you ran separate EGCs for the whole run, you'd still have to bond them to the metal boxes, so they would be bonded together at that common point anyways.

Top
#211917 - 11/22/13 08:26 PM Re: Common EGC for circuits in PVC raceway [Re: HotLine1]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
One grounding conductor per conduit sized for the largest circuit within the conduit Doesn't matter if its six different systems in it. Only exeception is isolated grounding. In a ground fault in a properly grounded system the fault will go back to the panel with that supplied the fault. Each service if grounded properly is bonded together for zero potential. So no one becomes a bonding jumper themselves
_________________________
"Live Awesome!" - Kevin Carosa