The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by Potseal
Today at 01:29 PM
Locked rotor, no burnout
by jraef
Today at 01:18 PM
Massive power outage South Australia
by Meadow
Today at 06:46 AM
short circuit??
by Meadow
Today at 06:43 AM
Norwegian power?
by Meadow
Today at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
3 registered (ghost307, geoff in UK, ComputerWizKid), 98 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#211573 - 10/28/13 12:35 PM Ballast question
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
I went to replace an electronic ballast in a standard 2'x 4'troffer. Once I opened it, I realized that it had only three tubes, not the four that I was expecting. The ballast had three blue wires and one red, assuming that the red was common to all three tubes and the each blue went to the opposite end of each tube.

The replacement ballast said on the box that it supports either three or four tubes, however the wiring diagram only showed it wired to four and the supporting documentation was just safety information, etc. This one looked more traditional: Two red wires, two blues and two yellows. My question is how to wire this thing to only three tubes. My experience has always been that tubes on these ballasts work in pairs. Any ideas?
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#211574 - 10/28/13 07:01 PM Re: Ballast question [Re: EV607797]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
If the wires don't match, you have the wrong ballast. Period.

Top
#211576 - 10/28/13 07:50 PM Re: Ballast question [Re: EV607797]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Some electronic ballasts don't work in pairs. Follow the diagram on the ballast and cap off the extra wire.

Top
#211577 - 10/28/13 09:53 PM Re: Ballast question [Re: EV607797]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
There may be more info on the internet. Search on the model number and see if there is an installation guide.
_________________________
Greg Fretwell

Top
#211578 - 10/28/13 10:31 PM Re: Ballast question [Re: twh]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
The old ballast is a instant start ballast while the new one is a rapid start. They do make the bulb ballasts or you could use a one bulb and a two bulb ballast. I'd be a bit concern with using a four bulb ballast with out specific documentation. I've seen the end result of a four bulb ballast in a three bulb fixture and the light out put between the three bulbs was noticeably different. I doubt those ballasts were listed for three lights though

A rapid start ballast can be wired in a instant start fixture but it has to be carefully rewired per the ballast diagram. Also, a rapid start ballast has a lag in lighting up. that could lead to a customer complaint. I'd suggest to advise the customer of the start up before hand. That's additional labor meaning added cost to someone. If possible, I'd return it and get a correct replacement ballast if practical
_________________________
"Live Awesome!" - Kevin Carosa

Top
#211581 - 10/29/13 07:14 AM Re: Ballast question [Re: EV607797]
electure Offline

Member

Registered: 12/24/00
Posts: 4225
Loc: Fullerton, CA USA
There are a number of electronic ballasts that will operate:

2 lamp ballasts (2 blue leads, 1 red) that will operate 1 lamp, just by capping off 1 of the blue leads.

3 lamp ballasts (3 blue leads, 1 red) that will operate 2 lamps, just by capping off 1 of the blue leads.

4 lamp ballasts (2 red, 2 blue, 2 yellow) that will operate 3 lamps with 1 of either the red or blue leads capped.

To retrofit a 4 lamp ballast into a 3 lamp fixture (originally equipped with a 3 blue, 1 red ballast), cap 1 of the red or blue leads.
Remove 1 of the jumpers from the lampholder to lampholder on the common side (originally red). The 2 yellows will go to the lampholders on the common end, 1 to the (originally red) lampholders, and 1 to the lampholder freed up by removing the jumper.

.........or just buy a 3 lamp ballast smile


Just like the black and white wires that will operate on 120 to 277 volts, they are meant to reduce the number of different ballasts you have to lug around on a day to day basis.









Top
#211582 - 10/29/13 09:07 AM Re: Ballast question [Re: EV607797]
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
Thanks, guys. I think I'll just buy the three-lamp ballast for these. I'm not looking forward to having to rewire the sockets, so a direct match will be the easiest solution.
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
#211803 - 11/16/13 01:57 PM Re: Ballast question [Re: EV607797]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Out my way, such units would be termed "independents."

They are less efficient than "master-slave" set-ups.

Independents are used when the layout doesn't allow a master-slave setup. A solo master would really waste energy.

So, that's the kind of ballast you need to be tracking down.

For these issues, never hesitate to phone/ internet Lithonia or the competition.




Edited by Tesla (11/16/13 02:01 PM)
_________________________
Tesla

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals