The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 259 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#211570 - 10/27/13 05:34 PM 400 amp remote service
watersparkfalls Offline

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
I am going to bring 400 amp service to a remote location, meter only no disco's till they terminate at their locations one to the house the second to the shop; The house has a ufer to establish service, however the shop doesn't have a ufer. Would I be required to establish its service at the remote location and bring 4 wires to the shop or can I still establish service at the shop and use 2 ground rods in lieu of ufer? Thanks sparky

2014 / 2011 NEC & Related Books and Study Guides
#211571 - 10/27/13 06:21 PM Re: 400 amp remote service [Re: watersparkfalls]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
Two separate buildings can have 2 services off the same drop or "may poled" from a single metered pole in the middle.
I would ask the AHJ how they feel about sending service conductors, building to building after the meter but I can't imagine how it isn't legal.
Greg Fretwell

#211583 - 10/29/13 12:43 PM Re: 400 amp remote service [Re: watersparkfalls]
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
If there is no Ufer available, and no footings being installed, then you must use any other available grounding electrode.

With nothing else (Ufer,water,steel,etc) you must install rods, ring, plate.