Can a GFCI receptacle be used as a disconnecting means for an out building (fed by only a single circuit) using the test button? I say no, but I saw this done over the weekend at a friend's place and he swears that it was inspected. I don't believe him.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
2017 / 2014 NEC & Related Books and Study Guides
#211366 - 10/08/13 12:32 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
IMHO, No!
_________________________
John
Top
#211372 - 10/08/13 07:20 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
NickD Offline
Member
Registered: 03/24/13
Posts: 46
Loc: Amish Country, PA
A GFCI CAN be used as a disconnecting means... that is what is supposed to do. This is not up for debate. Whether or not it is acceptable practice is the question.

A little more detail would be helpful, otherwise we'll be answering your question on a lot of assumptions.
There is a circuit, starting with a GFCI at the main building, which then runs to the out building?
Depending on the specific situation and the wiring in the outbuilding (the fact that it is only one circuit), I could see it being passed by an AHJ.


Edited by NickD (10/08/13 07:23 PM)
Top
#211377 - 10/08/13 07:30 PM Re: GFCI receptacle used as a disconnect? [Re: NickD]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
GFCI's are not listed as a service disconnect thus can not be used as one
_________________________
"Live Awesome!" - Kevin Carosa
Top
#211378 - 10/08/13 07:52 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The only exception to 225.38 is that a snap switch can be used in garages and out buildings on residential properties.
Nothing about a GFCI
_________________________
Greg Fretwell
Top
#211379 - 10/08/13 07:54 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Again & IMHO no it cannot be a disconnect. Yes, in theory pushing the 'test' button will open the circuit, but it is not manufactured, designed or intended as a disconnect.
_________________________
John
Top
#211380 - 10/08/13 07:58 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Sorry 225.36
_________________________
Greg Fretwell
Top
#211382 - 10/08/13 08:04 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Greg:
225.36 from 2011:
225.36 Suitable for Service Equipment. The disconnecting
means specified in 225.31 shall be suitable for use as
service equipment.
Exception: For garages and outbuildings on residential
property, a snap switch or a set of 3-way or 4-way snap
switches shall be permitted as the disconnecting means.

You are agreeing that a GFI cannot be used??
_________________________
John
Top
#211387 - 10/08/13 10:02 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Yes. It is not a snap switch and it is not suitable as service equipment as AK sparky pointed out.
_________________________
Greg Fretwell
Top
#211388 - 10/08/13 11:09 PM Re: GFCI receptacle used as a disconnect? [Re: gfretwell]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Test buttons don't always work on them
_________________________
"Live Awesome!" - Kevin Carosa
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals