The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/08/16 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 214 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#211364 - 10/08/13 12:19 PM GFCI receptacle used as a disconnect?
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
Can a GFCI receptacle be used as a disconnecting means for an out building (fed by only a single circuit) using the test button? I say no, but I saw this done over the weekend at a friend's place and he swears that it was inspected. I don't believe him.
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
2014 / 2011 NEC & Related Books and Study Guides
#211366 - 10/08/13 12:32 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
IMHO, No!
_________________________
John

Top
#211372 - 10/08/13 07:20 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
NickD Offline
Member

Registered: 03/24/13
Posts: 46
Loc: Amish Country, PA
A GFCI CAN be used as a disconnecting means... that is what is supposed to do. This is not up for debate. Whether or not it is acceptable practice is the question.

A little more detail would be helpful, otherwise we'll be answering your question on a lot of assumptions.
There is a circuit, starting with a GFCI at the main building, which then runs to the out building?
Depending on the specific situation and the wiring in the outbuilding (the fact that it is only one circuit), I could see it being passed by an AHJ.


Edited by NickD (10/08/13 07:23 PM)

Top
#211377 - 10/08/13 07:30 PM Re: GFCI receptacle used as a disconnect? [Re: NickD]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1296
Loc: Alaska
GFCI's are not listed as a service disconnect thus can not be used as one
_________________________
"Live Awesome!" - Kevin Carosa

Top
#211378 - 10/08/13 07:52 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The only exception to 225.38 is that a snap switch can be used in garages and out buildings on residential properties.
Nothing about a GFCI
_________________________
Greg Fretwell

Top
#211379 - 10/08/13 07:54 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Again & IMHO no it cannot be a disconnect. Yes, in theory pushing the 'test' button will open the circuit, but it is not manufactured, designed or intended as a disconnect.
_________________________
John

Top
#211380 - 10/08/13 07:58 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Sorry 225.36
_________________________
Greg Fretwell

Top
#211382 - 10/08/13 08:04 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Greg:
225.36 from 2011:
225.36 Suitable for Service Equipment. The disconnecting
means specified in 225.31 shall be suitable for use as
service equipment.
Exception: For garages and outbuildings on residential
property, a snap switch or a set of 3-way or 4-way snap
switches shall be permitted as the disconnecting means.

You are agreeing that a GFI cannot be used??
_________________________
John

Top
#211387 - 10/08/13 10:02 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Yes. It is not a snap switch and it is not suitable as service equipment as AK sparky pointed out.
_________________________
Greg Fretwell

Top
#211388 - 10/08/13 11:09 PM Re: GFCI receptacle used as a disconnect? [Re: gfretwell]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1296
Loc: Alaska
Test buttons don't always work on them
_________________________
"Live Awesome!" - Kevin Carosa

Top