ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
fuse rejectors
by NORCAL. 03/29/17 01:44 AM
Old decora style outlets
by NORCAL. 03/29/17 01:41 AM
NFPA stuff
by gfretwell. 03/28/17 08:08 PM
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,734 Are you busy
166,637 Re: Forum
160,788 Need opinion
Who's Online Now
0 registered members (), 63 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#211301 - 10/03/13 04:36 PM Circuit Design in Canada  
Stuart_Urban  Offline
New Member
Joined: Aug 2013
Posts: 5
England
Comparing the Canadian Electrical Code (CEC) with the British Wiring Regulations I can see that both documents require consideration of voltage drop and current carrying capacity when designing circuits. However within the CEC there does not seem to be any consideration of the disconnection time of the circuit breaker in the event of a fault to ground (as explained in the link below).

So my query is can anyone you tell me if when designing circuits within Canada consideration of the disconnection time of circuit breakers is part of the design process.

http://www.electrical-installation.org/enwiki/Automatic_disconnection_for_TN_systems


Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#211308 - 10/03/13 10:33 PM Re: Circuit Design in Canada [Re: Stuart_Urban]  
twh  Offline
Member
Joined: Mar 2004
Posts: 903
Regina, Sask.
I think that is among the purposes of the requirement that all equipment have CSA approval for the purpose for which it is used. Disconnection time would be dealt with in the standard for the approval of the overcurrent devices.

If you intend to export a piece of equipment to Canada, to get CSA certification, all components must be CSA approved. If certification is to be obtained after the equipment arrives in Canada, all non-approved components must be replaced. This includes fuses and breakers.


#211318 - 10/04/13 08:38 PM Re: Circuit Design in Canada [Re: Stuart_Urban]  
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,392
Vienna, Austria
I think the question goes deeper than this. Under serious circumstances, a German electrician would in fact calculate, whether branch circuit conductors of a certain size would actually allow an overcurrent protection device with a certain current rating and trip curve to trip within the required time based on the loop impedance/short circuit current.

This is most interesting where breakers/fuses are used as earth fault protection (which is the fact in all Canadian and US circuits that are not on a GFI). An extensive run of small wire, fed by a small transformer might actually have such a high impedance that an earth fault wouldn't be noticed as a short circuit by the breaker any more but merely as an overload.

BTW, I can't remember if we've covered this before, but do all US/Canadian breakers have both a thermal and a magnetic fast-trip? If there's only a thermal trip, trip time is likely a moot point anyway.


#211357 - 10/08/13 05:22 AM Re: Circuit Design in Canada [Re: Stuart_Urban]  
Stuart_Urban  Offline
New Member
Joined: Aug 2013
Posts: 5
England
From the little knowledge I have of Canadian installations circuit breakers have a magetic and thermal trip. Disconnection times can alsoe be achieved by the use of a RCD/GFCI where ground loop impedance is too high to achieve disconnection in the required time.

I have found the following in the CEC 10-500:

“The path to ground from circuits, equipment, or conductor enclosures shall be permanent and continuous, shall have ampacity to conduct safely any currents liable to be imposed on it, and shall have impedance sufficiently low to limit the voltage above ground and to facilitate the operation of the overcurrent devices in the circuit.”

And in the CEC Handbook guidance it states that this is normally achieved by a sufficiently low impedance such that the overcurrent device is presented with a fault current of 5 times it’s rating. Which in effect is the 0.4 second requirement of BS 7671.

What I would like to know is does anybody bother working this out in Canada? Are GFCIs routinely used on circuits?

Last edited by Stuart_Urban; 10/08/13 05:24 AM.


Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7596 MB (Peak: 0.8920 MB) Zlib enabled. Server Time: 2017-03-29 13:18:23 UTC