#211254 - 09/30/13 10:26 AM ground fence
Bravo Offline
Member
Registered: 05/04/10
Posts: 30
Loc: NY, USA
Hello,

I have a metal chain link fence inside a building that surrounds process equipment. Does the fence have to be grounded? I cant find req's in the NEC.

Thanks in advance

Top
2017 / 2014 NEC & Related Books and Study Guides
#211255 - 09/30/13 11:36 AM Re: ground fence [Re: Bravo]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
A general rule that is not always fleshed out well in the language is that you should bond anything that is likely to be energized. If this fence is not near any energized conductors, it probably does not need to be bonded.

As an aside, it is probably fairly well "grounded" by the posts in the ground but that is not the same as bonded.

Places where I see fences bonded is where there is significant radiated power. This can be a radio/TV transmitter or just a big distribution transformer farm.

680 will also require that a fence be bonded if it is <5' from the water.
_________________________
Greg Fretwell
Top
#211258 - 09/30/13 04:29 PM Re: ground fence [Re: Bravo]
Alan Belson Offline
Member
Registered: 03/23/05
Posts: 1803
Loc: Mayenne N. France
A friend bought an old farmhouse cheap, cheap because a new 400,000 volt line from a new atomic reactor passed close by [200 yards, heading for Italy]- and destroyed local realty values. Now the poco has bonded the neighbor's entire sheet metal barns and machinery shed. Is that why? Should he do the same to his barn, do you think?
_________________________
Wood work but can't!
Top
#211259 - 09/30/13 04:48 PM Re: ground fence [Re: Bravo]
mbhydro Offline
Member
Registered: 02/21/03
Posts: 347
Loc: Winnipeg MB Canada
I wonder if they are worried about tingle voltage affecting the livestock so that's why the POCO paid for the grounding?
Top
#211260 - 09/30/13 06:18 PM Re: ground fence [Re: Bravo]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I have a 250KV and two 48KV lines running behind my house and I can't seem to detect any strange voltage problems. I tried every YouTube trick I have seen to light a fluorescent tube with no joy.
I even tried stringing 100' of THHN directly under the poles with various terminations or simply floating ... nothing.

It is a little disappointing actually. I thought I could get free lights for my boat house, virtually directly under the line.
_________________________
Greg Fretwell
Top
#211261 - 09/30/13 06:45 PM Re: ground fence [Re: Bravo]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Not on YouTube, but:
Changing 10'HO lamps in a sign, my 'ground man' yells on the two-way.."the bulb is lit!!".

End of the tube was 3'+/- from a 13.2 primary. It was not 'bright' but it was glowing!

OOOPS!
_________________________
John
Top
#211262 - 09/30/13 06:55 PM Re: ground fence [Re: Bravo]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The poles are marked 115' but I assume 15' or more is in the ground. I suppose I could climb up a little closer and try. wink
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals