#211229 - 09/27/13 08:09 AM Devices in Unoccupied Spaces
Bravo Offline
Member
Registered: 05/04/10
Posts: 30
Loc: NY, USA
Is it a code violation for put receptacles in a unoccupied spaces? I have air return chase plenums that are accessible but are classified as unoccupied.

Thanks in advance

Dean
Top
2017 / 2014 NEC & Related Books and Study Guides
#211231 - 09/27/13 10:08 AM Re: Devices in Unoccupied Spaces [Re: Bravo]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
It has to be in a metal wiring method.
More important is what do you plan to plug in to that receptacle. You can only have equipment "necessary for their direct action upon, or sensing of, the contained air" (300.22(B))and I would want to see the listing. A cord is probably not going to be allowed unless it is plenum rated.

_________________________
Greg Fretwell
Top
#211239 - 09/27/13 06:13 PM Re: Devices in Unoccupied Spaces [Re: Bravo]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
dbravo:
If you proposed a compliant wiring method and what are the receptacles for?

I have seen a compliant receptacle installed for monitoring (testing) equipment use by service techs.
_________________________
John
Top
#211245 - 09/28/13 11:19 AM Re: Devices in Unoccupied Spaces [Re: Bravo]
MarkC10 Offline
Member
Registered: 09/22/13
Posts: 43
Loc: CA, Inland Empire
I'd think it would be fine .. FAU's up in attic spaces require a power source which are not meant to be use by any occupant .. as long as the power source is readily accessible for maintenance or service and conform to other necessary NEC guidelines as far as approved boxes,fittings etc .. really It just can't be buried or covered up.
_________________________
Anyone claiming to know everything about Electrical, is wrong.
Top
#211246 - 09/28/13 12:25 PM Re: Devices in Unoccupied Spaces [Re: Bravo]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
"Unoccupied space" is not an issue in the NEC. They only address the physical concerns (environmental air handling space, damp/wet location, hazardous location etc).
_________________________
Greg Fretwell
Top
#211355 - 10/07/13 08:41 PM Re: Devices in Unoccupied Spaces [Re: Bravo]
NickD Offline
Member
Registered: 03/24/13
Posts: 46
Loc: Amish Country, PA
"Rules" in this area are a bit fuzzy. Receptacles are "not permitted" in areas like the space above a suspended or drop ceiling, and yet, there are devices (condensate pumps etc) that are plug-in as OE, and they sometimes have to go into these spaces.

To answer the OP's question literally and directly, though, it is no code violation to put ANYTHING in an "unoccupied" space. As soon as the last person leaves a room... it becomes an "unoccupied space". wink


Edited by NickD (10/07/13 08:47 PM)
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals