The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 61 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#211034 - 09/06/13 06:51 PM RV park remote meter centers need main disconnect?
bigpapa Offline
Member

Registered: 03/18/06
Posts: 75
Loc: canada
I am looking for opinions on this RV park install, or possibly some code rules that are less obvious.


First we will install a main service with breakers and feeders for several meter stacks. The meter stacks will then feed a bunch new 50A 120/240V RV pedestals. Each pedestal will have its own meter and breaker in the stack.


The arrangement is pretty much the same as you would see in a typical residential high rise where there are usually no main disconnects in the meter closets.

The difference is that since our meter closet kiosks are distributed outdoors throughout the park they are technically different buildings. I am leaning towards including the disconnects because of this.

I talked to the inspector but he wouldn't comment on design issues.
They don't really have time for this when I call at 3:30 on a Friday I gather.

If anyone cares to comment please do.

Top
2014 / 2011 NEC & Related Books and Study Guides
#211042 - 09/08/13 01:27 PM Re: RV park remote meter centers need main disconnect? [Re: bigpapa]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
72-104 allows USEI and you could treat each distribution centre as a service. It would be tempting to do this because of the issue of different potentials between ground and neutral over distances (and cable cost). If you ran ACWU with a separate ground, I'm not aware of any rule requiring a disconnect at each building where it isn't a service.

Perhaps the inspector wouldn't comment on design issues because the inspectors don't agree on whether a main disconnect is required on a sub-panel where the sub panel is in a separate building and this is similar.

Be aware that entrance switches can't be in public areas unless "adequate precautions are taken to prevent interference", under 9.26.1.3 of the National Building Code of Canada.

Top
#211049 - 09/08/13 07:39 PM Re: RV park remote meter centers need main disconnect? [Re: twh]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
There's no breakers in the pedistals?
_________________________
"Live Awesome!" - Kevin Carosa

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals