The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 299 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#210979 - 08/29/13 04:23 PM AFCI's
sparkync Offline

Registered: 10/17/02
Posts: 811
Loc: NC
I've got a permit on a detached RV garage right next to the house it belongs to, ( had to run it all in conduit). The house already has been inspected and has power. While checking on my job, I thought I would just look at the electrical panel for the house, since it is right next to the garage I will be working on. I noticed that there were no AFCI's on Bathroom recepts., microwave recept., wash machine recept., kitchen lights, garage outlets, and dishwasher and disposal multiwire circuit. It's been a while since I've wired a new house, but I was thinking that everything except maybe the baths and kitchen had to have AFCI's. Obviously I was wrong. Don't have my new code with me right now. I sort of see all the above being ok, since they are GFI protected after the first outlet, except "kitchen lights". Don't understand that one. The only one's that did have AFCI's were, Master bedroom outlets, Bedroom outlets, and living room . Any comments?? Think the inspector just missed it?

2014 / 2011 NEC & Related Books and Study Guides
#210981 - 08/29/13 04:58 PM Re: AFCI's [Re: sparkync]
Trick440 Offline

Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
We have only been required to ARc protected bedrooms and smoke detectors. Nothing else ...yet.
Shake n Bake

#210984 - 08/29/13 07:46 PM Re: AFCI's [Re: sparkync]
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
This is from the 2011 NEC:

210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall
be protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.

Note that 'kitchen' is not mentioned, so the kitchen lights are not mandatory for AFCI protection.

What NEC is in effect in your area?

#210985 - 08/29/13 08:03 PM Re: AFCI's [Re: sparkync]
schenimann Offline

Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
We are on 2011. Our inspectors are pretty lenient on what you need to have arc faults on. I usually end up with 7-9 breakers for a whole house on the general use recepts. I have not been failed for not having something on arc faults.