The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
1 registered (ampherder), 63 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#210953 - 08/28/13 08:12 AM Siemens meter stack neutral difference
steener Offline
New Member

Registered: 11/03/05
Posts: 8
Loc: Green Bay,WI, USA
I have a customer with a Siemens Modular Metering service on a strip mall. The tenants have been complaining of flickering lights, GFCI's unable to reset, among other issues. After a little research I found what I believe to be the source of the problem. There is a fused 800A main ahead of three meter stacks which has the correct bonding from what is visible. At the first stack there is a difference that varies between 10 and 20 volts between the EGC and the neutral. Between A,B, and C phases and the EGC is about 122 volts, but to neutral its 108, 118, 145 volts. It seems there is some resistance in the neutral buss connection somehow between the main disconnect and the first meter stack.
This morning I shut the main off and re-tourqed the single bolt joint on the horizontal buss. No change.
Has anyone experienced this? Any options aside from replacement?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#210957 - 08/28/13 12:37 PM Re: Siemens meter stack neutral difference [Re: steener]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Did you check all the terminations within the main disco?
Neutrals & GECs/EGCs at the bonding point?

Is the issue within one or all of the meter stacks?
_________________________
John

Top
#210959 - 08/28/13 02:14 PM Re: Siemens meter stack neutral difference [Re: steener]
steener Offline
New Member

Registered: 11/03/05
Posts: 8
Loc: Green Bay,WI, USA
Only visually as far as tightness. They are directly behind the POCO's connections. I did check the voltage between the neutral/gnd buss within the main disco and the chassis and read 0 volts. Between the same buss in the main disco and the neutral bar in the meter stack I get the same fluctuating voltage as in the meter stacks alone.
The issue exists within all of the meter stacks.


Edited by steener (08/28/13 02:21 PM)

Top
#211002 - 08/31/13 09:31 PM Re: Siemens meter stack neutral difference [Re: steener]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
There may be an intermittent connection across a set of Bus Jumpers for the Grounded Conductor, as the recorded Voltage between Lines A, B & C to the EGC shows 122V; but Lines A, B & C to N show 108V, 118V and 145V.

If so, it is likely due to an incorrectly installed Belleville Washer, or the Bolt / Nut were never Torqued.

--Scott (EE)
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#211005 - 09/01/13 01:23 PM Re: Siemens meter stack neutral difference [Re: steener]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Neutrals tend to be lightly loaded because they carry the unbalanced load and that is a very high voltage difference. Maybe the bolt and nut are missing.

Top
#211008 - 09/01/13 11:02 PM Re: Siemens meter stack neutral difference [Re: steener]
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
Is the grounded conductor aluminum? I found a problem once with a feeder where the conductor degraded inside the insulation.
We tore into a wall and found a bubbled spot where the conductor was overheating. Good idea to shut it down and check everything. An overheated connection could break loose
and BOOM! Unrelated but check for missing buss supports also. I just opened an older Federal Pacific pull section to find 2 of the critical main buss supports missing.

Top
#211009 - 09/02/13 02:34 PM Re: Siemens meter stack neutral difference [Re: twh]
wa2ise Offline
Member

Registered: 11/29/02
Posts: 769
Loc: Oradell NJ USA
Originally Posted By: twh
Neutrals tend to be lightly loaded ...


True for resistive loads, but if there's lots of computer equipment, their power supplies will draw pulses of current that don't match up with other current pulses on the other phases. AKA harmonics. In this case the neutral gets really hammered.

Top