The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 245 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#210949 - 08/27/13 08:22 PM PF correction capacitor blowing fuses
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
I have a customer that has a Sprague 300KVAR PF correction capacitor that is blowing 2 of the internal fuses. I have not had much interaction with this product. Can anyone tell me what would cause the fuses to continuously blow?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#210950 - 08/27/13 10:33 PM Re: PF correction capacitor blowing fuses [Re: Merlin]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
A shorted capacitor would be my guess.

Top
#210961 - 08/28/13 07:28 PM Re: PF correction capacitor blowing fuses [Re: Merlin]
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
That was in fact the case. One capacitor was shorted.

Top
#213039 - 03/11/14 12:51 PM Re: PF correction capacitor blowing fuses [Re: Merlin]
afyon Offline
New Member

Registered: 03/10/14
Posts: 2
Loc: toronto
@Merlin, Sometimes we forget the simplest of reasons for something happening. Mostly we’re too focused on a particular component that we skip the nearby components. However, I was wondering how your capacitor might have gotten short. Did it get blown up or was it short because of some connection issues? It is a great help if you can post how your capacitor was getting shorted and what might’ve been the reasons that kept you distracted from this issue. This information can then later be used by anyone else who is in a similar situation. It gets easy to diagnose for others this way.


Edited by afyon (03/11/14 12:51 PM)

Top
#213048 - 03/14/14 07:01 PM Re: PF correction capacitor blowing fuses [Re: afyon]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
Afyon,
Capacitors that are constantly subjected to full mains voltage are prone to failure, it's just something that happens.
When the dielectric insulation between the "plates" of the capacitor fail, you then end up with a dead short between the plates, causing short circuit current to flow and the circuit protection to operate.

If you've ever seen inside a large capacitor, it's like a large roll, that is how you can have such a large capacitance in a physically small component.

I see a lot of capacitor failures with things like single phase air compressors, where the centrifugal switch can jam and leave the start winding and the capacitor in circuit, instead of switch over to the run winding.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#213087 - 03/19/14 03:55 AM Re: PF correction capacitor blowing fuses [Re: Merlin]
geoff in UK Offline
Member

Registered: 12/30/02
Posts: 169
Loc: UK
Many failures of electronic equipment are due to large electrolytic capacitors shorting or, occasionally, going OC.
Often the fault can be visually identified by bulging of the case or leakage of electrolyte.

Top
#213303 - 04/06/14 08:15 AM Re: PF correction capacitor blowing fuses [Re: Merlin]
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
Thank you Trumpy, for responding to the question from Afyon. Another thing that I found during this situation that I should have thought of. This capacitor bank has 5 capacitors per phase (3 phases). Trying to conserve on a costly capacitor for the customer, I only replaced one. I should have put more thought into this, as I was called back a month later with more fuses blown. I have always understood capacitors to be like batteries, never change only one but change all that are linked together. Therefore, I had to go back and replace the other four on that phase to eliminate anymore problems.

Thanks for the great discussion gentlemen. Its always great to find people that are willing help others.