#210779 - 08/04/13 11:11 AM Convert 240V to 208V?
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Can a 240V-3ph panelbd (with a wild leg) be easily converted to 208V-3ph? (assume that any connected equipment can operate on 208V)
Top
Work Gear for Electricians and the Trades
#210780 - 08/04/13 11:36 AM Re: Convert 240V to 208V? [Re: cgw]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Is this panel fed from the utility co? If so, then the POCO is where the modifications are started.

_________________________
John
Top
#210781 - 08/04/13 02:03 PM Re: Convert 240V to 208V? [Re: cgw]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
If you are just running motors it probably doesn't matter and a lot of other equipment can be jumpered t0 run 208 or 240.

Like John says, this is a PoCo option. They will need to add another transformer, probably replacing the small one you have too.
The typical center tapped delta uses a smaller transformer for the wild leg and they only use 2, leaving one side of the delta open (AKA Delta Vee)
Expect a fee for this.

I bet your transformers look like this.




_________________________
Greg Fretwell
Top
#210782 - 08/04/13 02:04 PM Re: Convert 240V to 208V? [Re: cgw]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
You want this
_________________________
Greg Fretwell
Top
#210785 - 08/04/13 10:02 PM Re: Convert 240V to 208V? [Re: cgw]
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
The direct answer to the question you actually asked is, no its not hard because its the same panel. After that, see the above answers.
Top
#210789 - 08/05/13 03:06 PM Re: Convert 240V to 208V? [Re: cgw]
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Everything up to the panelbd will be replaced (the entire service). There is no question on the line side.
I assume (I am going over to look at it tomorrow) that only the 3 phase loads are connected to the middle bus (in this case maybe a rooftop unit - it is retail). So when it becomes 208V the middle phase will be un-balanced. In addition - the panelbd is currently the service entrance. That will no longer be the case after the change (there will be a line side main disconnect). So the neutral needs to be separated (I'm thinking out-loud). Any other considerations?
Top
#210790 - 08/05/13 03:49 PM Re: Convert 240V to 208V? [Re: cgw]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
You can swap some breakers around and balance the service once you get real 3p wye in there.
You can get a head start by going in with your clamp when they are running their normal load and tagging the current on each circuit. Then you will have a starting point for the rebalance.
We used to have to do that in computer rooms sometimes because each machine might have significant single phase loads and the luck of the draw might get some unwanted imbalance.
_________________________
Greg Fretwell
Top
#210791 - 08/05/13 06:50 PM Re: Convert 240V to 208V? [Re: cgw]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Once you get an OK from the POCO, and they do their thing at the pole, you should be good to go.

You may find 2 pole, 240 volt circuits on the 'B' phase, and whatever 3 phase equipment you have on the site.

As to maintaining a balance, Gregs head start is a good plan.
_________________________
John
Top
#210792 - 08/05/13 07:10 PM Re: Convert 240V to 208V? [Re: cgw]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
We didn't see much in computer rooms but it usually will be the L/N loads he has to move. They are all on A/C now.
_________________________
Greg Fretwell
Top
#210793 - 08/05/13 07:18 PM Re: Convert 240V to 208V? [Re: cgw]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Over the years, I saw many panels with nothing on 'B' phase.

Most were in factorys that were vacated, and 'quick' converted to other uses. A lot of breaker blanks with 'RED LEG' written on them.
_________________________
John
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals