#210674 - 07/19/13 08:44 PM AFCI on sump pump??
sparkync Offline
Member
Registered: 10/17/02
Posts: 809
Loc: NC
A sump pump is being installed in a finished basement where the water heater, wash machine, and dryer will be located. Will this have to be on a AFCI breaker?? It will be bad if the breaker trips because of "nuisance" tripping while they are on vacation, and the water heater or water pipes break:(
Of course this could possibly happen in any scenario, but what does the code say?? thanks...
Top
2017 / 2014 NEC & Related Books and Study Guides
#210675 - 07/19/13 11:27 PM Re: AFCI on sump pump?? [Re: sparkync]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I would leave an area or room around the sump pump "unfinished" but it would still need a GFCI.
In my house, it would be a regular circuit and "come and get me copper"
_________________________
Greg Fretwell
Top
#210677 - 07/20/13 10:06 AM Re: AFCI on sump pump?? [Re: sparkync]
sparkync Offline
Member
Registered: 10/17/02
Posts: 809
Loc: NC
Greg, even if is a single recpt. so that nothing else can be plugged in, it's required to be GFCI?? Thanks
Top
#210678 - 07/20/13 10:17 AM Re: AFCI on sump pump?? [Re: sparkync]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
There is no exception regarding a single receptacle,

A GF trip is not 'good' for an active sump pump, but the possibility of a shock hazard has priority.
_________________________
John
Top
#210679 - 07/20/13 10:23 AM Re: AFCI on sump pump?? [Re: sparkync]
sparkync Offline
Member
Registered: 10/17/02
Posts: 809
Loc: NC
another question related to this same job. When a ceiling is dropped in a full basement, do the joist still have to be bored out for the wires? Sorry not up to digging in the code this morning, hitting on about 4 out of 8 cylinders:)
Thanks on the reply about the GFI. I didn't see it in time...


Edited by sparkync (07/20/13 10:25 AM)
Top
#210681 - 07/20/13 10:49 AM Re: AFCI on sump pump?? [Re: sparkync]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
sparkync:

From the '11 NEC:
"(C) Cables Through Spaces Behind Panels Designed to
Allow Access. Cables or raceway-type wiring methods, installed behind panels designed to allow access, shall be
supported according to their applicable articles. '

That said, there is nothing within Art 334 that says you have to drill.

However, your local AHJ may have another opinion. The "physical damage" can be subjective.
_________________________
John
Top
#210682 - 07/20/13 11:28 AM Re: AFCI on sump pump?? [Re: sparkync]
sparkync Offline
Member
Registered: 10/17/02
Posts: 809
Loc: NC
thanks John, I don't think (in my opinion) that it is going to subject to physical damage above ceiling tile... That's in my opinion smile hope the AHJ has the same opinion
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals