The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 258 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#210577 - 07/11/13 08:33 AM AC wiring and 250.122
BigB Offline
Member

Registered: 03/31/04
Posts: 725
Loc: Tucson, AZ USA
We are seeing a lot of "mini split" AC units. As an example, let's say we have a mini split with an MCA of 11 amps, and a maximum fuse or circuit breaker of 25 amps per the nameplate. The wiring method is Romex. Wiring the unit with 14/2 would satisfy the MCA, however I believe it would violate 250.122 due to the 25 amp OCPD. To comply with 250.122, using Romex it seems we would need 10/2, no? Am I missing something?


Edited by BigB (07/11/13 08:34 AM)

Top
2014 / 2011 NEC & Related Books and Study Guides
#210579 - 07/11/13 12:43 PM Re: AC wiring and 250.122 [Re: BigB]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
You have to determine the OCP that you are installing to determine the EGC for the circuit.

Using the nameplate MAX of 25 OCP would require #12. This is based on 250.122 table in '11 NEC as I read it.
_________________________
John

Top
#210581 - 07/11/13 04:58 PM Re: AC wiring and 250.122 [Re: BigB]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Originally Posted By: BigB
We are seeing a lot of "mini split" AC units. As an example, let's say we have a mini split with an MCA of 11 amps, and a maximum fuse or circuit breaker of 25 amps per the nameplate. The wiring method is Romex. Wiring the unit with 14/2 would satisfy the MCA, however I believe it would violate 250.122 due to the 25 amp OCPD. To comply with 250.122, using Romex it seems we would need 10/2, no? Am I missing something?


BigB...The first sentence of 250.122(A) says that in no case shall the EGC be required to be larger than the circuit conductors supplying the equipment...

Top
#210582 - 07/11/13 05:01 PM Re: AC wiring and 250.122 [Re: HotLine1]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Originally Posted By: HotLine1
You have to determine the OCP that you are installing to determine the EGC for the circuit.

Using the nameplate MAX of 25 OCP would require #12. This is based on 250.122 table in '11 NEC as I read it.



I use the Minimum Circuit Ampacity to size my branch circuit conductors for an AC unit...

Top
#210585 - 07/11/13 08:17 PM Re: AC wiring and 250.122 [Re: BigB]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Please note that the 2014 edition will have changes to this requirement in air conditioning article.

Top
#210586 - 07/11/13 08:33 PM Re: AC wiring and 250.122 [Re: shortcircuit]
BigB Offline
Member

Registered: 03/31/04
Posts: 725
Loc: Tucson, AZ USA
Ah so I was missing something. The scary part is I am pretty sure I knew that at one time. Getting old is no fun.


Edited by BigB (07/11/13 08:33 PM)

Top
#210587 - 07/11/13 08:52 PM Re: AC wiring and 250.122 [Re: BigB]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Perhaps a little clearer....

BigB example is 14/2NM, but he said 25 amp OCP, using the nameplate max figure.

Using the max OCP, a #12 EGC would be required, so using NM he has to use 12/2.

Yes, the EGC does not have to be larger than the circuit conductors, 'oversize' EGC to my knowledge is not available.

IMHO, I believe that he did not read Table 250.122 where the amperage col. jumps from 20 amps for #12, and 60 amps for #10.
_________________________
John

Top
#210588 - 07/11/13 08:56 PM Re: AC wiring and 250.122 [Re: BigB]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Originally Posted By: BigB
Ah so I was missing something. The scary part is I am pretty sure I knew that at one time. Getting old is no fun.


I agree with the getting old and memory loss...

Top
#210590 - 07/11/13 09:01 PM Re: AC wiring and 250.122 [Re: BigB]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
short:
Ditto!!
_________________________
John

Top
#210591 - 07/11/13 09:04 PM Re: AC wiring and 250.122 [Re: HotLine1]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Originally Posted By: HotLine1
Perhaps a little clearer....

BigB example is 14/2NM, but he said 25 amp OCP, using the nameplate max figure.

Using the max OCP, a #12 EGC would be required, so using NM he has to use 12/2.



I'm not sure I follow you Hotline...

When doing AC units the nameplate has all the info for sizing the branch circuit wiring...and sizing the overcurrent device.

For example...if the nameplate gives a MINIMUM BRANCH CIRCUIT AMPACITY of 30amps and a MAXIMUM BRANCH CIRCUIT OVERCURRENT DEVICE of 50amps...

I will wire the unit with 10-2 romex and connect it to a 50amp breaker.

Follow me?

shortcircuit

Top