The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 208 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#210540 - 07/08/13 03:55 PM Weird voltages on transformer
SafetyWired Offline
Member

Registered: 07/08/13
Posts: 44
Loc: Pa, USA
Today had a call that parking lot lights were not illuminating. Here is the set-up: Primary V 208/120 3P feeding a 75KVA transformer. Steps up to 480/277v.
From transformer, circuit goes to a photo cell controlled contactor, which than energizes a panel with lighting circuits.
Photo control working correctly. Contactor opens and closes correctly. However...with contactor CLOSED I have these voltages from phase to ground on HV side. A:210 B:340 C:340. When contactor is OPEN I have A:177 B 178 C:160 Phase to phase whether A-B or A-C or B-C is 479-481V no matter if contactor is open or closed. I have never seen this before. Any theories.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#210541 - 07/08/13 04:16 PM Re: Weird voltages on transformer [Re: SafetyWired]
SafetyWired Offline
Member

Registered: 07/08/13
Posts: 44
Loc: Pa, USA

Top
#210542 - 07/08/13 04:20 PM Re: Weird voltages on transformer [Re: SafetyWired]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
Is your 277/480 neutral grounded?

Top
#210543 - 07/08/13 04:23 PM Re: Weird voltages on transformer [Re: twh]
SafetyWired Offline
Member

Registered: 07/08/13
Posts: 44
Loc: Pa, USA
Yes. This system has been in place since 2002. All of a sudden parking lot lights do not go on. I checked bond in xfmr, and also followed electrode back to main. First thing I checked after reading screwy voltages.

I believe it is in the xfmr coils themselves. I removed HV wires off xfmr lugs for giggles to see if voltage would change with nothing connected on that side. Voltages were the same.

Top
#210544 - 07/08/13 04:40 PM Re: Weird voltages on transformer [Re: SafetyWired]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
With 480 volts on the lines, the neutral/ground voltage isn't possible without a bad neutral or ground. I assume your lighting is 277 volts. What else can it be?

Top
#210546 - 07/08/13 04:44 PM Re: Weird voltages on transformer [Re: twh]
SafetyWired Offline
Member

Registered: 07/08/13
Posts: 44
Loc: Pa, USA
Originally Posted By: twh
With 480 volts on the lines, the neutral/ground voltage isn't possible without a bad neutral or ground. I assume your lighting is 277 volts. What else can it be?


It is 277v lighting. Please clarify your response, I do not quite understanding what you are saying the way it is worded...Thanks blush


Edited by SafetyWired (07/08/13 04:45 PM)

Top
#210547 - 07/08/13 05:08 PM Re: Weird voltages on transformer [Re: SafetyWired]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
I assume the lights not working is related to the odd voltage.

With a 480/277 system, you cannot have another voltage to ground besides 277 unless the neutral or ground wire is bad. That would also explain the lights not working.

It's my best guess.

Top
#210548 - 07/08/13 05:34 PM Re: Weird voltages on transformer [Re: twh]
SafetyWired Offline
Member

Registered: 07/08/13
Posts: 44
Loc: Pa, USA
Originally Posted By: twh
I assume the lights not working is related to the odd voltage.

With a 480/277 system, you cannot have another voltage to ground besides 277 unless the neutral or ground wire is bad. That would also explain the lights not working.

It's my best guess.


This could mean the coils ground too than...correct?

Top
#210549 - 07/08/13 05:40 PM Re: Weird voltages on transformer [Re: SafetyWired]
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
Sure sounds like secondary neutral bonding to me.

Top
#210550 - 07/08/13 05:51 PM Re: Weird voltages on transformer [Re: JoeTestingEngr]
SafetyWired Offline
Member

Registered: 07/08/13
Posts: 44
Loc: Pa, USA
Neutral is bonded to frame with copper band, on xfmr than lugged electrode runs from chassis to main disc. bond. I were to run a second electrode temp from bond in disc to xfmr frame, and I still do not have 277...would it mean the neutral/ground is open in the transformer itself?