The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
52 minutes 53 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#210452 - 06/24/13 09:46 AM 250.122 Parallel circuits
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Question :
3 sets of (480V 3 phase )600 MCM off a 1200 amp feeder OCP. to a Mcc. in Tray cable.
Ground wire in each not correctly sized for 1200 amps (3/0)
from factory stock comes (#3) Can 3/0 ground run with tray
cover it??
Yoopersup

Top
2014 / 2011 NEC & Related Books and Study Guides
#210453 - 06/24/13 10:51 AM Re: 250.122 Parallel circuits [Re: Yoopersup]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
IMO, no. All equipment ground conductors in each cable must be full sized. Fault currents may not divide equally depending on where the fault is and this could exceed the rating of the equipment ground if not full sized. AFAIK, there is no exception to the requirement.


Edited by Tom (06/24/13 10:52 AM)
Edit Reason: spelling
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#210454 - 06/24/13 12:44 PM Re: 250.122 Parallel circuits [Re: Yoopersup]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
2011 NEC 250.122(F) seems to allow a single EGC in a tray...

or if under certain conditions, the tray can be the EGC...

Top
#210455 - 06/24/13 02:29 PM Re: 250.122 Parallel circuits [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
292.60 2011 NEC
Cable trays SHALL be permitted to be used as Equipment grounding conductors.
Then refers you to 250.96 70-118.
Other grounds then are supplemental.
Supplemental grounds are additional grounds & are then they still required to be full size???
2011 McGraw Hills handbook page 517 states:
The last sentance of 250.122 (A) points out that metal raceways and cable armor recognized as an equipment grounding conductors: Table 122 does not apply to them.
Yoopersup

Top
#210456 - 06/24/13 03:32 PM Re: 250.122 Parallel circuits [Re: Yoopersup]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Where did you get the information that "Other Grounds are Supplemental?"

Top
#210457 - 06/24/13 03:32 PM Re: 250.122 Parallel circuits [Re: Yoopersup]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If the tray meets the cross section requirement in table 392.60(A), you agree that this is "where continuous maintenance and supervision" and they tray is connected to the equipment at both ends with a 3/0, it is legal.
I agree supplemental grounding is just that, more than you require.

The handbook warns about assemblies of conductors may have insufficient grounding conductors when used as parallel sets.

Quote:
Cable assemblies are manufactured in standard conductor size configurations, and the equipment grounding conductor in a cable is properly sized for some circuit arrangements but not necessarily for all parallel circuit arrangements. Where the cable is used in large-capacity parallel circuits, it is necessary to ensure that the equipment grounding conductor in each cable is sized as required by Table 250.122, based on the size of the overcurrent device protecting the circuit.



Each parallel set (in a raceway) shall be 250.122.
The cable tray gives you more latitude the way I read it.
_________________________
Greg Fretwell

Top
#210458 - 06/24/13 06:04 PM Re: 250.122 Parallel circuits [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Section 392.60(A)
Grounding and Bonding
(A) Metallic Cable Trays
. Metallic cable trays shall be
permitted to be used as equipment grounding conductors
where continuous maintenance and supervision ensure
that qualified persons service the installed cable tray
system and the cable tray complies with provisions of this section. Metallic cable trays
that support electrical conductors shall be grounded as required for conductor enclosures
in accordance with 250.96 and Part IV of Article 250. Metal cable tray containing only
non-power conductors shall be electrically continuous, through approved connections or
the use of a bonding jumper not smaller than a 10 AWG.
Informational Note: Examples of non-power conductors include nonconductive optical fiber
cables and Class 2 and Class 3 Remote Control Signaling and Power Limited Circuits.
Analysis of Change:
Section 392.60 (392.7(A), 2011 NEC was revised to require the metal cable tray systems
to be bonded when used with non-power conductors.

250.96 (A) Bonding other Enclosures.
Metal raceways ,Cable trays, Cable Armor, Cable sheath ,Enclosers, Frames, Fittings and other metal non-current carrying parts that serve as Equipment grounding conductors with or without the use of Supplementary grounding conductors Shall be bonded where necessary .
Yoopersup

The (Tray or RMC) or anything approved by 250.118 by itself
that can carry the fault current well do the trick.
So is anything else Supplementay.

Top
#210459 - 06/24/13 06:57 PM Re: 250.122 Parallel circuits [Re: Yoopersup]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
So...are you going to run a separate equipment grounding conductor or use the tray?

Top
#210460 - 06/24/13 07:32 PM Re: 250.122 Parallel circuits [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Both / Ground wire attached to side of tray probably 4/0 with listed & labeled ground clamps & all conduits coming off the tray attached to it. All non contentious tray sections bonded together via 4/0 also.
Always interested in other electricians take on things! Not everything in the Code is clear to me anyway!