The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (sparkyinak), 201 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#21044 - 01/26/03 11:06 AM Dishwasher and Garbage Disposal = BX or RX?
Currently Offline
Member

Registered: 04/21/02
Posts: 54
Loc: TN
Just pulled a permit to do electrical on my new kitchen cabinets. Original wiring was the old cloth romex with no ground with some nasty problems that cropped up like 21 devices on a 15 amp circuit and on and on...

Dishwasher is on dedicated circuit with octogon box in back of cabinet. Do I wire from the box to dishwasher with BX or RX?

Garbage disposal will be wired on GFI circuit (2 duplexes and GFI with half horse disposal on 20 amp circuit on left circuit from sink) Should I use BX from octogon to disposal or leave as plastic romex.

I have seen both in the past and want to do it "right" the first time. Each side of the sink will be on its respective 20 amp breaker. All outlets and switches are rated 20 amps.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#21045 - 01/26/03 11:15 AM Re: Dishwasher and Garbage Disposal = BX or RX?
HouseOfPower Offline
Member

Registered: 01/25/03
Posts: 11
Loc: Houston Texas
The dishwaswher and disposal should be on dedicated 20 amp circuits, but not on a GFI. They both need to be switched and I put a plug inside the cabinet, then use a romex connector and a pigtail out of the disposal to plug into th plug.

Top
#21046 - 01/26/03 06:34 PM Re: Dishwasher and Garbage Disposal = BX or RX?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I would install a receptacle, no GFCI for the GD or DW. The GD cord has to be "identified as suitable" for garbage disposals, and between 18 & 36" long. See article 422.16(B)(1). The DW cord, 36-48". See 422.16 (B)(2). It makes connecting & servicing easier.

[This message has been edited by Redsy (edited 01-26-2003).]

Top
#21047 - 01/26/03 07:42 PM Re: Dishwasher and Garbage Disposal = BX or RX?
dugmaze Offline
Member

Registered: 12/18/00
Posts: 46
Loc: St. Louis
I've heard that a GFCI would continually trip out.

Top
#21048 - 01/27/03 10:29 AM Re: Dishwasher and Garbage Disposal = BX or RX?
Currently Offline
Member

Registered: 04/21/02
Posts: 54
Loc: TN
Thanks to all, appreciate the feedback.

Top