The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by HotLine1
Today at 07:07 PM
Locked rotor, no burnout
by jraef
Today at 01:18 PM
Massive power outage South Australia
by Meadow
Today at 06:46 AM
short circuit??
by Meadow
Today at 06:43 AM
Norwegian power?
by Meadow
Today at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 296 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#210212 - 06/03/13 12:50 PM Large Feeder Tap
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Suppose I had a large feeder running across a building (3 sets 600) and I wanted to tap the feeder with 1 set #1. Just tapping one set of the large feeder is correct and practical?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#210213 - 06/03/13 01:12 PM Re: Large Feeder Tap [Re: cgw]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
Without all the technical info of what you hooking up and what the existing load,If it meets the tap requirements of article 240 and not overload the original load, and meets other applicable requirements, I don't see a problem
_________________________
"Live Awesome!" - Kevin Carosa

Top
#210215 - 06/03/13 03:50 PM Re: Large Feeder Tap [Re: cgw]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I have a problem with it. The whole idea of paralleled conductors is that you are going to balance the load across the conductors equally (same size, length etc)
If you unequally load one conductor, you are defeating the O/C protection.
The only way I see this as legal is if you group them, make your tap and then break them out again.

I will look for a code reference
_________________________
Greg Fretwell

Top
#210216 - 06/03/13 04:00 PM Re: Large Feeder Tap [Re: cgw]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
This is the commentary from the handbook

Quote:
Where individual conductors are tapped from conductors in parallel, the tap connection must include all the conductors in parallel for that particular phase. Tapping into only one of the parallel conductor would result in unbalanced distribution of tap load current between parallel conductors, resulting in one of the conductors carrying more than its share of the load, which could cause overheating and conductor insulation failure. For example, if a 250-kcmil conductor is tapped from a set of two 500-kcmil conductors in parallel, the splicing device must include both 500-kcmil conductors and the single 250-kcmil tap conductor.
_________________________
Greg Fretwell

Top
#210220 - 06/03/13 05:51 PM Re: Large Feeder Tap [Re: cgw]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
I stand corrected! I missed it was a parallel run of 600's. Excuse me why I sit here looking stupid and eat my crow sandwich...
_________________________
"Live Awesome!" - Kevin Carosa

Top
#210221 - 06/03/13 06:46 PM Re: Large Feeder Tap [Re: cgw]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
It is not insurmountable, you just need a big, 7 hole, Polaris connector.
_________________________
Greg Fretwell

Top
#210222 - 06/03/13 09:54 PM Re: Large Feeder Tap [Re: cgw]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
Split bolts mastic pads and Super 88 will do the trick....
anyone

Lol!
_________________________
"Live Awesome!" - Kevin Carosa

Top
#210225 - 06/04/13 06:52 AM Re: Large Feeder Tap [Re: gfretwell]
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Originally Posted By: gfretwell
It is not insurmountable, you just need a big, 7 hole, Polaris connector.


If the feeder is for a transformer, would it be easier to connect (the tap) to the transformer primary connections.