#210212 - 06/03/13 12:50 PM Large Feeder Tap
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Suppose I had a large feeder running across a building (3 sets 600) and I wanted to tap the feeder with 1 set #1. Just tapping one set of the large feeder is correct and practical?
Top
Work Gear for Electricians and the Trades
#210213 - 06/03/13 01:12 PM Re: Large Feeder Tap [Re: cgw]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Without all the technical info of what you hooking up and what the existing load,If it meets the tap requirements of article 240 and not overload the original load, and meets other applicable requirements, I don't see a problem
_________________________
"Live Awesome!" - Kevin Carosa
Top
#210215 - 06/03/13 03:50 PM Re: Large Feeder Tap [Re: cgw]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I have a problem with it. The whole idea of paralleled conductors is that you are going to balance the load across the conductors equally (same size, length etc)
If you unequally load one conductor, you are defeating the O/C protection.
The only way I see this as legal is if you group them, make your tap and then break them out again.

I will look for a code reference
_________________________
Greg Fretwell
Top
#210216 - 06/03/13 04:00 PM Re: Large Feeder Tap [Re: cgw]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
This is the commentary from the handbook

Quote:
Where individual conductors are tapped from conductors in parallel, the tap connection must include all the conductors in parallel for that particular phase. Tapping into only one of the parallel conductor would result in unbalanced distribution of tap load current between parallel conductors, resulting in one of the conductors carrying more than its share of the load, which could cause overheating and conductor insulation failure. For example, if a 250-kcmil conductor is tapped from a set of two 500-kcmil conductors in parallel, the splicing device must include both 500-kcmil conductors and the single 250-kcmil tap conductor.
_________________________
Greg Fretwell
Top
#210220 - 06/03/13 05:51 PM Re: Large Feeder Tap [Re: cgw]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
I stand corrected! I missed it was a parallel run of 600's. Excuse me why I sit here looking stupid and eat my crow sandwich...
_________________________
"Live Awesome!" - Kevin Carosa
Top
#210221 - 06/03/13 06:46 PM Re: Large Feeder Tap [Re: cgw]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
It is not insurmountable, you just need a big, 7 hole, Polaris connector.
_________________________
Greg Fretwell
Top
#210222 - 06/03/13 09:54 PM Re: Large Feeder Tap [Re: cgw]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Split bolts mastic pads and Super 88 will do the trick....
anyone

Lol!
_________________________
"Live Awesome!" - Kevin Carosa
Top
#210225 - 06/04/13 06:52 AM Re: Large Feeder Tap [Re: gfretwell]
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Originally Posted By gfretwell
It is not insurmountable, you just need a big, 7 hole, Polaris connector.


If the feeder is for a transformer, would it be easier to connect (the tap) to the transformer primary connections.
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals