ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
fuse rejectors
by NORCAL. 03/29/17 01:44 AM
Old decora style outlets
by NORCAL. 03/29/17 01:41 AM
NFPA stuff
by gfretwell. 03/28/17 08:08 PM
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,801 Are you busy
166,691 Re: Forum
160,835 Need opinion
Who's Online Now
0 registered members (), 78 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 3 1 2 3
#210161 - 05/30/13 05:40 PM Manholes  
akmaster  Offline
Member
Joined: Jun 2012
Posts: 70
alaska
Is there a article in the code that requires a slope of 3% oriented to the manhole? Or does it cover that at all?

Please quote article if possible.

Thank you.

Greg


Don't drive and TEXT! Drive now TALK LATER!

2017 / 2014 NEC & Related Books and Study Guides

#210163 - 05/30/13 05:58 PM Re: Manholes [Re: akmaster]  
akmaster  Offline
Member
Joined: Jun 2012
Posts: 70
alaska
I believe article 310 covers manholes..


Don't drive and TEXT! Drive now TALK LATER!

#210173 - 05/31/13 08:03 PM Re: Manholes [Re: akmaster]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Is the manhole owned by a utility company or privately owned? Is this a service wire, feeder wire from 1 building to another? Maybe the guys need a little more info.


#210175 - 05/31/13 08:20 PM Re: Manholes [Re: akmaster]  
akmaster  Offline
Member
Joined: Jun 2012
Posts: 70
alaska
It is one of many manholes on an ethanol project...it will contain Medium voltage cables (4160) fiber and control and DC circuits..the are 8'x 8'x8'. They have a base and a top...
the specs call for a 0.3% slope TOWARDS the manhole..

I did not find that requirement anywhere in the code..

It seems they will need racks inside to rack the cables as well..

Thanks,
Greg


Don't drive and TEXT! Drive now TALK LATER!

#210176 - 05/31/13 09:24 PM Re: Manholes [Re: akmaster]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
Toward the manhole? Is this also the storm drain system?


Greg Fretwell

#210182 - 06/01/13 02:36 PM Re: Manholes [Re: akmaster]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,


Check sec. 110 V of the NEC, that talks about manholes and their construction also sec. 490 talks about voltage over 600. You also might have to refer to the National Safety Code. Most utilities follow those rules. I might have an old NESC book around, I would have to look.


#210186 - 06/01/13 04:39 PM Re: Manholes [Re: akmaster]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,803
Brick, NJ USA
This may say something: From '08 Handbook:

"110.70 General.
Electrical enclosures intended for personnel entry and specifically fabricated for this purpose shall be of sufficient size to provide safe work space about electrical equipment with live parts that is likely to require examination, adjustment, servicing, or maintenance while energized. Such enclosures shall have sufficient size to permit ready installation or withdrawal of the conductors employed without damage to the conductors or to their insulation. They shall comply with the provisions of this part.
Exception: Where electrical enclosures covered by Part V of this article are part of an industrial wiring system operating under conditions of maintenance and supervision that ensure that only qualified persons monitor and supervise the system, they shall be permitted to be designed and installed in accordance with appropriate engineering practice. If required by the authority having jurisdiction, design" (documentation may be required)

Last edited by HotLine1; 06/01/13 04:41 PM. Reason: added text in parenthesis

John

#210208 - 06/03/13 02:17 PM Re: Manholes [Re: akmaster]  
akmaster  Offline
Member
Joined: Jun 2012
Posts: 70
alaska
Thanks for the replies. @ Greg...yes towards the manhole...

@hotline...thanks I will take a look...

I can not find any requirement regarding slope of 0.3 percent towards the manhole for conduits...

does this include the whole run from man hole to man hole?

regards

Greg


Don't drive and TEXT! Drive now TALK LATER!

#210230 - 06/04/13 02:15 PM Re: Manholes [Re: akmaster]  
akmaster  Offline
Member
Joined: Jun 2012
Posts: 70
alaska
Another question: Is it not a requirement that manholes with high voltage are required to have the cover labeled "DANGER HIGH VOLTAGE"?

Thanks

GW

Last edited by akmaster; 06/04/13 02:15 PM.

Don't drive and TEXT! Drive now TALK LATER!

#210231 - 06/04/13 02:25 PM Re: Manholes [Re: akmaster]  
akmaster  Offline
Member
Joined: Jun 2012
Posts: 70
alaska
One more...Does the Manhole cover have to be grounded?


Don't drive and TEXT! Drive now TALK LATER!

Page 1 of 3 1 2 3

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.023s Queries: 16 (0.004s) Memory: 0.8179 MB (Peak: 1.0003 MB) Zlib enabled. Server Time: 2017-03-30 02:41:08 UTC