The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 322 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#209924 - 05/14/13 05:38 PM Portable Welder grounding
akmaster Offline
Member

Registered: 06/11/12
Posts: 70
Loc: alaska
Do Portable welders like an 8-pack, or single large welding machines on trailers have to be grounded to earth with a GEC? We have a lot of them on the job and I am having trouble locating anything about a GEC. These are hardwired from a 220 and 480 VAC panels..transformer for 120/208 has no GEC to X/O bond from case of xfmr.

Thanks for any input.

Greg
_________________________
Don't drive and TEXT! Drive now TALK LATER!

Top
2014 / 2011 NEC & Related Books and Study Guides
#209927 - 05/14/13 06:40 PM Re: Portable Welder grounding [Re: akmaster]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Again, why would you want to do it? To create a danger?
_________________________
Greg Fretwell

Top
#209930 - 05/15/13 06:24 AM Re: Portable Welder grounding [Re: akmaster]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Stop. Think. Think again.

What are you trying to accomplish?

"Grounding" is not some mysterious voodoo. It's actually pretty straightforward - though I will credit illiterate engineers and code committees for making the topic as clear as mud.

Let's look at the types of situations when we think of "grounding." Where does the term come from?

Grounding. Ground. The earth beneath our feet is an obvious source. What's that got to do with anything?

Well, we NORMALLY want everything we touch to be at the same potential, lest current flow somewhere we don't want current to flow - like, say, through our bodies. So, we tie everything together, making sure that everything we touch is 'safe.' While often called 'grounding,' this is more correctly called 'bonding.'

Electricity, simply put, wants to 'go home,' wants to return to where it (the potential difference) was created. It will take all paths, in accordance with Ohm's law, greatly preferring an easy path to a hard one. Think about that for a moment.

Electricity is "created" at transformers, generators, and welders. We want the power to go out, do its' work, and come back - and the most effective way is to make sure there's only ONE path to follow.

In welding, this means one wire is placed near the work, and the other is firmly attached to the work. The idea is to make electricity jump the gap between, and melt the steel. We call the 'return' wire a 'ground,' but it's not. It's more like a 'negative' or a 'neutral.' Language fails me.

Since Ohm's law applies, we can touch the workpiece without fear, as the electricity will vastly prefer to 'go home' through that big fat wire, than to flow through us.

Now, what about 'ground rods?' The ONLY electricity that wants to return to the earth we stand on is electricity that came from there. We have two names for this 'natural' electricity: static electricity and lightning. That's the ONLY electricity that needs to 'return to earth.'

Top
#209931 - 05/15/13 08:20 AM Re: Portable Welder grounding [Re: akmaster]
akmaster Offline
Member

Registered: 06/11/12
Posts: 70
Loc: alaska
Hi,
Thanks for the replies. I have an engineer on the job who is insiting that these welders have to have an external ground. They are fed with a 3 wire circuit..Two hots and a ground. The machine gets its ground from the source. The welders use their ground lead attached to the building steel or the work piece.

One engineer says he has the GEC and EGC in the same conduit feeding the main 480V panel..then from a breaker to that panel feeding a step down transformer..that does not have a GEC bonded to the X/O..which I have already confirmed that either building steel, water pipe or ground rod is required.

I am simply confirming that these 8 pack welders do NOT require a ground rod.

Thanks for your patience and assistance.

regards

Greg
_________________________
Don't drive and TEXT! Drive now TALK LATER!

Top
#209934 - 05/15/13 10:06 AM Re: Portable Welder grounding [Re: akmaster]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
My little buzz box has an EGC connected to the case of the welder but the secondary is not grounded.