#209923 - 05/14/13 04:46 PM Portable Generator Grounding
akmaster Offline
Member
Registered: 06/11/12
Posts: 70
Loc: alaska
Any portable generator that is hard wired to equipment or devices must be grounded to earth as I understand OSHA. If there are cord and plug connections then no ground rod is required. Is this correct?

Thanks

Greg


Edited by akmaster (05/14/13 04:46 PM)
_________________________
Don't drive and TEXT! Drive now TALK LATER!
Top
2017 / 2014 NEC & Related Books and Study Guides
#209925 - 05/14/13 06:12 PM Re: Portable Generator Grounding [Re: akmaster]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
A 'cord & plug' connection is the 'EGC' (equipment grounding conductor) It is not a GEC, nor a Bond.

The earth ground for a 'portable' (3-8+/-KW) is a much debated topic and common practice is to just run it.

_________________________
John
Top
#209926 - 05/14/13 06:39 PM Re: Portable Generator Grounding [Re: akmaster]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I have always questioned why you would even want to ground a truly portable generator (cord loads only).
There is a modicum of safety in having the generator ungrounded. With no ground reference, there is no danger from a fault to ground.
_________________________
Greg Fretwell
Top
#209928 - 05/14/13 07:22 PM Re: Portable Generator Grounding [Re: akmaster]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
gfretwell:

I had this debate as an EC back in '05 regarding portable light towers. Diesel, 4-6 1000 watt MH floods, and 2-120 volt GFIs on board. (Towable units)

The AHJ wanted grd rods at each unit. I had 65 units spread out over grass, paved parking lots, quarry auxilary parking & a few municipal streets.

Discussions, and a polite request for an article number eliminated the rods.

_________________________
John
Top
#209929 - 05/14/13 08:45 PM Re: Portable Generator Grounding [Re: akmaster]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
There are a lot of small generators that do not bond the neutral, most notably the Honda inverters.
This really only becomes an issue if you try to hook one to a 3 wire transfer switch.

I lifted the bond on my 5.5KW genset because my plan is to connect it with my breaker interlock. I already have the pigtail mounted on the side of the house for it. So far we have not had an outage worth filling it with gas.
(2 years for me and 3 years for the guy I bought it from)
My UPS's carried me through the last one. It was funny sitting there with both PCs running and the TV, satellite etc still going. If the kitchen light had not gone off I might not have even noticed.

_________________________
Greg Fretwell
Top
#209932 - 05/15/13 08:31 AM Re: Portable Generator Grounding [Re: akmaster]
akmaster Offline
Member
Registered: 06/11/12
Posts: 70
Loc: alaska
OSHA says that any hard wired cord connected supply from the generator has to have a ground rod bonded to the frame of the generator. If you have cord and plug connected only, no ground rod is required.

Here is the article:

http://click.infospace.com/ClickHandler.ashx?du=www.osha.gov%2f...%2fgrounding_port_generator.pdf&ru=http%3a%2f%2fwww.osha.gov%2fOshDoc%2fdata_Hurricane_Facts%2fgrounding_port_generator.pdf&ld=20130515&ap=1&app=1&c=snapdov3a.5&s=snapdov3a&coi=771&cop=main-title&euip=70.195.4.96&npp=1&p=0&pp=0&pvaid=6d1c792782f74931a5905afa937d6da7&ep=1&mid=9&hash=A1E9D9E485178B3B64C4E759ABAE3F08

Thank you,

Greg
_________________________
Don't drive and TEXT! Drive now TALK LATER!
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals