The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 106 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#209806 - 04/29/13 10:49 AM Elevator Motor
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
A typical hydraulic elevator with a 20HP code F motor. 72A running and 166A start up.
The question is - is the 166A start up just the normal motor start current or is it something that should be taken in account for:
1. circuit size?
2. generator sizing?
3. voltage drop?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#209807 - 04/29/13 11:45 AM Re: Elevator Motor [Re: cgw]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The biggest issue of the 3 is the generator. Other than that I would just design to 125% of the FLA. Voltage drop would be an issue if the branch circuit is very long. There are a number of voltage drop calculators around but if this is existing, it is hard to beat simply measuring the voltage at each end. Just be sure the motor is running when you check the line side end to get an accurate measurement of that leg.