The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Potseal 7
Who's Online
0 registered (), 279 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#209645 - 04/15/13 05:58 AM MC cable in a damp location
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Do we have any information that makes it clear about running MC cable in a damp location. I can find wet locations and dry but nothing on a damp location?
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#209646 - 04/15/13 07:52 AM Re: MC cable in a damp location [Re: George Little]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6786
Loc: Brick, NJ USA
George:
No, I can't see anything that is clear on this.
IMHO, the sheath materials should be clarified,between the steel and aluminum.

I have seen the aluminum sheath deteriorate in a few installs from condensation.
_________________________
John

Top
#209651 - 04/15/13 11:33 AM Re: MC cable in a damp location [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
What is the question? If the MC is wet location rated, doesn't that encompass damp locations?

I looked at the MFG page for the Southwire MC-XHHW (one of the wet location MCs), it says that is an XHHW-2 conductor and that conductor is listed wet and damp (330.10(A)11(c)). I assume you would derate from the 75c column in a damp location like you do in a wet one.
_________________________
Greg Fretwell

Top
#209652 - 04/15/13 12:27 PM Re: MC cable in a damp location [Re: George Little]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Greg...

My Ugly's has XHHW-2 as a 90c conductor for derating purposes.

Even XHHW is rated 90c.
_________________________
Tesla

Top
#209655 - 04/15/13 02:46 PM Re: MC cable in a damp location [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I guess I "assumed" wrong wink

The box of EZ-MC I have says you derate at 75c when wet but that is not exactly the same stuff. Southwire did not even reference that on their page. Maybe it was a THHN/THWN product that was replaced by the XHHW
_________________________
Greg Fretwell

Top
#209701 - 04/18/13 08:17 PM Re: MC cable in a damp location [Re: George Little]
mikethebull Offline
Member

Registered: 03/18/07
Posts: 101
Loc: Rhode Island
330.10 (A)(11) gives conditions for MC in wet locations.

Top
#209704 - 04/18/13 08:24 PM Re: MC cable in a damp location [Re: George Little]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Greg...

That XHHW-2 stuff is creeping in all over the place.

I first saw it with aluminum feeders. Now, it's popping up around stranded copper, from time to time.
_________________________
Tesla

Top
#209708 - 04/19/13 12:41 PM Re: MC cable in a damp location [Re: George Little]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6786
Loc: Brick, NJ USA
George:
Are you refering to the sheath, or the conductor insulation?
_________________________
John

Top
#209709 - 04/19/13 01:23 PM Re: MC cable in a damp location [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
The aluminum armor is considered suitable for wet locations if the wrapper and conductors are wet rated. I understand that salt air can eat it but when you are talking about the sea shore, galvanized rigid metal is not that great either.
_________________________
Greg Fretwell

Top
#209710 - 04/19/13 04:11 PM Re: MC cable in a damp location [Re: George Little]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Greg...

Carrying that thought further, any aluminum bussing installed near the ocean is at hazard for AlCl3 'rust.'

Aluminum is normally considered 'rust proof' because run-away corrosion does not occur -- unless chloride ions are present.

But, aluminum is, in fact, prone to ultra-rapid 'rusting' / oxidation. Bare aluminum metal oxidizes promptly in air. It acquires a THIN coat of Al2O3 -- aka alumina. It's so thin that you can see right through it. Unlike iron oxide rust, alumina expands to lock up tight, creating an air tight seal.

If salt air is misting in, the chlorine displaces the oxygen in the alumina. Now the metal loses its sheild. AlCl3 shrinks like common rust. Given enough time, aluminum metal becomes pitted -- with cruddy AlCl3 ( it's yellow ) crystals at the surface.

I've witnessed bussing that's picked up a 3 volt drop right at the rails (under load) over a twenty-year period.

The solution is to kill power, buff the crud off the rails, clean the breaker-rail contacts and re-assemble.

Where it's an issue, copper bussing is worth the premium. Copper does not rapidly react with salt air like aluminum.

This issue is why aluminum can't be totally trusted below grade. Some American soils are absolutely laden with old ocean salts. (Nevada, California, Utah, Arizona,...) So you can't trust aluminum to stay bonded as part of a GEC system.
_________________________