#20957 - 01/24/03 05:52 PM HyPotting
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
What are some of the typical HyPot voltages and time for 1/C 5KV and 15KV cables with shielding ?

Is their a 'Rule of Thumb '?
Top
Work Gear for Electricians and the Trades
#20958 - 01/24/03 07:52 PM Re: HyPotting
gramps Offline
Member
Registered: 08/25/02
Posts: 112
Loc: ohio
2 times the rated voltage times 75% for 1 minute....record the reading....take another reading for 10 minutes...record that reading.

divide the first reading into the second reading....EASA recommends the answer should be 2.0 or higher.....but, 1.5 is prolly o.k.
Top
#20959 - 01/24/03 10:45 PM Re: HyPotting
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
There are different levels for new versus maintenance testing, and 100% or 133% insulation.

One chart is http://www.kerite.com/catalog/catalogfiles/DC_field_testing_power.htm

Be Careful. You’re charging up fairly big capacitor(s) in the process. The test-set instruction manual is a good reference.




[This message has been edited by Bjarney (edited 01-25-2003).]
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals