#209333 - 03/24/13 01:01 AM I hope nobody reads this book
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
There was a Dayton instruction booklet in the box with my new motor. It was pretty thick and I hoped it had all the wiring diagrams for Dayton motors or something else useful.
Nope, just the regular stuff in 3 languages but there was a chart labeled "minimum wire size".
It is designed to hold starting current (LRA?) under 5%. That is some scary stuff, like a 1/2 HP motor 50 feet from the panel requires #8.

I hope inspectors don't start calling this a 110.3(B) requirement.
_________________________
Greg Fretwell
Top
2017 / 2014 NEC & Related Books and Study Guides
#209334 - 03/24/13 04:41 AM Re: I hope nobody reads this book [Re: gfretwell]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Such a wire schedule must have been written by an attorney.

BTW, induction motors always pull the system voltage down more than 5% during start up -- though for a very brief moment of time.

After all, an induction motor -- upon connection -- is a bolted short.

_________________________
Tesla
Top
#209340 - 03/24/13 09:57 AM Re: I hope nobody reads this book [Re: gfretwell]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Greg, you read the instruction manual? Must we take your "man" card away?...
_________________________
"Live Awesome!" - Kevin Carosa
Top
#209348 - 03/24/13 11:00 AM Re: I hope nobody reads this book [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
In order for a 110.3(B) issue, the mentioned document must be made available to the inspector? Right?

Now, IF you wired it with #12 at 60', would you provide this document to the inspector?

On the other side of the fence, how many inspectors would ask for motor mfg docs, as opposed to looking at the nameplate data??
_________________________
John
Top
#209351 - 03/24/13 11:17 AM Re: I hope nobody reads this book [Re: gfretwell]
NickD Offline
Member
Registered: 03/24/13
Posts: 46
Loc: Amish Country, PA
That's how instruction manuals are these days... nothing but a little bit of useless information repeated over and over in several different languages. I think the record number I've seen is nine (9!). shocked
Of course... the English section is usually laughably flawed, in spite of it all. clap

Makes you wonder if they'll ever consider amending or dismissing 110.3(B).... rolleyes


Originally Posted By HotLine1
In order for a 110.3(B) issue, the mentioned document must be made available to the inspector? Right?

Now, IF you wired it with #12 at 60', would you provide this document to the inspector?

On the other side of the fence, how many inspectors would ask for motor mfg docs, as opposed to looking at the nameplate data??


+1!


Edited by NickD (03/24/13 11:20 AM)
Top
#209353 - 03/24/13 11:33 AM Re: I hope nobody reads this book [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
My last request for mfg info related to equipment being installed in a cabinet shop. Relocated from another town, and 95% is 'aged'. Lack of any readable nameplate data (in english), or sign of any NRTL labeling, I requested that some data is required.

Long story short, wow did they supply data; in english and korean! A manilla file folder for each piece of equipment at least 25+pages in each. Useful?? Time will tell.
_________________________
John
Top
#209354 - 03/24/13 11:35 AM Re: I hope nobody reads this book [Re: sparkyinak]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Originally Posted By sparkyinak
Greg, you read the instruction manual? Must we take your "man" card away?...


Well I didn't read it until 4 days after I installed the motor, does that count?
_________________________
Greg Fretwell
Top
#209373 - 03/24/13 10:27 PM Re: I hope nobody reads this book [Re: gfretwell]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Originally Posted By gfretwell
Well I didn't read it until 4 days after I installed the motor, does that count?
I guess we can let it slide this time... thumbs
_________________________
"Live Awesome!" - Kevin Carosa
Top
#209391 - 03/25/13 09:02 PM Re: I hope nobody reads this book [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Well Gents, it appears that as inspectors we are going to have to cave in a little bit when it comes to Signs in Article 600.33.

I can just see the expression on the installers face when I ask him for the instructions. Then when I tell him it is required he is going to Freak.
_________________________
George Little
Top
#209398 - 03/25/13 10:45 PM Re: I hope nobody reads this book [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
George
As for coming up with the instructions,

The technology has arrived. A young guy would Google it up and show it to you on the phone. wink
_________________________
Greg Fretwell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 85 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals