#209312 - 03/23/13 09:14 AM Re: Sump Pump
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Do sump pumps have to be on GFCI protection?
Top
Work Gear for Electricians and the Trades
#209316 - 03/23/13 10:48 AM Re: Sump Pump [Re: harold endean]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Depends...
Top
#209317 - 03/23/13 04:57 PM Re: Sump Pump [Re: harold endean]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Harold:
A single receptacle is OK in my book, w/o GF.
_________________________
John
Top
#209322 - 03/23/13 05:28 PM Re: Sump Pump [Re: harold endean]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
They make GFCI receptacles with audible alarms now. These work great in areas that require GFCI receptacles and you have concern for lost power on pumps, refridgerators or similar equipment.
Top
#209327 - 03/23/13 09:41 PM Re: Sump Pump [Re: harold endean]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
I would like to see some more answers before I reply to my own post. smile
Top
#209331 - 03/23/13 11:12 PM Re: Sump Pump [Re: harold endean]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The law?

There is not a lot of wiggle room in 210.8

Quote:
(5) Unfinished basements for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like
Exception to (5): A receptacle supplying only a permanently installed fire alarm or burglar alarm system shall not be required to have ground-fault circuit-interrupter protection.

If this is a crawlspace, unfinished basement or garage, the only 120v 15/20a receptacle that gets an exception is an alarm circuit.
Even a dedicated single is not OK unless you come up with an alarm to plug in it.
You could get away with rewiring it to 240 from what I read.

I am glad I don't need to explain that to a home owner.

On the other hand this is a lot more dangerous than what we protect from in swimming pools.
I see;
.A flood
..The pump stopped
...A homeowner standing in ankle deep water with a screwdriver in his hand trying to figure out why the pump isn't running.

In a perfect world there would be a dead face GFCI at the top of the steps, just feeding the sump pump. If it won't hold, you are done.
If it was indicating (noise or light) you have something.
_________________________
Greg Fretwell
Top
#209339 - 03/24/13 09:56 AM Re: Sump Pump [Re: harold endean]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Greg,

When I see a BA/FA transformer it is either in a duplex receptacle that is over 6' or higher. (no GFI required). I have seen them in single receptacles. Then the installer usually tie warps the trans to the box.

Would you allow this, a duplex receptacle with the phase leg strap snipped so that the top half of the duplex is dead, but the bottom half is live. This way the installer can still use the 6-32 screw to hold the trans in place. Also you should make the installer paint the top half black or something like write DEAD on the top half.
Top
#209343 - 03/24/13 10:16 AM Re: Sump Pump [Re: harold endean]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
I have another question/scenario, What about a finished basement with a bathroom. There is a ejector/grinder pump for the basement toilet. It is behind the finished wall into the "Unfinished" area of the basement. Is GFI protection required for the receptacle? If it is a duplex? Single?
Top
#209344 - 03/24/13 10:42 AM Re: Sump Pump [Re: harold endean]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Harold:
The split duplex with the 'dead' half has been a subject of discussion many times. Technically, I'll take a shot that it is 'wrong', as there is a single device that is readilly available. My opinion; show me why & I may agree. The wall wart transformer is (according to mfg) be mounted via the plate screw. Would I have an issue with tie-wraps? Probably not.

Back to the sump & ejector pumps; IMHO, the scenario Greg wrote above is a safety issue. IMHO, I have not heard of anyone saying 'the guy in xxx town wants GFI'.

_________________________
John
Top
#209352 - 03/24/13 11:32 AM Re: Sump Pump [Re: harold endean]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Quote:
When I see a BA/FA transformer it is either in a duplex receptacle that is over 6' or higher. (no GFI required).


Where is there a 6' exception to 210.8(5)?

I am not sure I would get too excited about a duplex, serving the transformer for a BA/FA. If NEMA would catch up with the code, the wall wart would have screw tabs spaced for the cover screws on a single receptacle.

_________________________
Greg Fretwell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals