#209270 - 03/20/13 05:34 PM Sub Panel with no neutrals
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Probably everyone has seen it. Main panel is full so a sub panel is set next to it, however it is not supplied with a neutral feeder, only hots and a bond. The circuits all enter the main panel first and only the hots are extended into the sub panel, the neutrals and grounding wires are landed in the first panel. Does a violation exist?
Top
2017 / 2014 NEC & Related Books and Study Guides
#209271 - 03/20/13 07:49 PM Re: Sub Panel with no neutrals [Re: BigB]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Neutral-less panels are as common as dust in industrial settings. These are designed to fit within the 'web' of a vertical I beam/ column. Since such panels are also very, very, likely to feed 3-phase loads, the neutral doesn't get a lot of action, anyway.

You'll find them listed in Square D catalogs.

They are frowned upon elsewhere. The operative assumption being that subsequent players are going to be so stupid as to not correctly land neutral conductors. The 'savings' from omission of a neutral path into the adjacent panel are insignificant.

I must be a rare electrician, I've never seen the set-up described. I don't work the heavy industrial side of the street.


Edited by Tesla (03/20/13 07:50 PM)
_________________________
Tesla
Top
#209272 - 03/20/13 07:59 PM Re: Sub Panel with no neutrals [Re: Tesla]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Perhaps the sub-panel was set up to run only phase to phase loads. That's not a code violation.
_________________________
"Live Awesome!" - Kevin Carosa
Top
#209274 - 03/20/13 08:22 PM Re: Sub Panel with no neutrals [Re: sparkyinak]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
I may have to eat my words. More to follow...
_________________________
"Live Awesome!" - Kevin Carosa
Top
#209275 - 03/20/13 08:26 PM Re: Sub Panel with no neutrals [Re: BigB]
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
"the neutrals and grounding wires are landed in the first panel. Does a violation exist?"

I can't quote the code ref, however I remember from school that grounded and ungrounded must originate from same panel.

And the grounding seems weird to run back to first panel too.

I could be wrong, since I have no ref(too tired to look right now) but expressing my humble opinion.

H20
Top
#209278 - 03/20/13 08:53 PM Re: Sub Panel with no neutrals [Re: sparkyinak]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
I have seen them before but can't swear they were to code. I'm gonna keep digging because it has my cariousity. So far, in article 215 Feeders, there is a minimum grounded conductor size shall not be smaller the required by 250.122. However I'm not sure what they mean by that
_________________________
"Live Awesome!" - Kevin Carosa
Top
#209279 - 03/20/13 08:53 PM Re: Sub Panel with no neutrals [Re: BigB]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
The neutral does not need to extend beyond the service disconnect enclosure.
Back when there were real computer rooms, we never brought the neutral to the computer panels. They had a "building" panel supplying the lights and the 120v loads but none of them were computer related, everything was 208 or 240 L/L loads. The 120v monitors were plugged into a service outlet in the CPU that ran off an isolation transformer.

There was still a neutral style bar in the panels but it had a green wire feeding it usually with a yellow tracer and was the isolated grounding conductor that went to the machines.
The can and the raceways were bonded to the "bare wire" ground (the one with green only if it was insulated).

This fell out of vogue about the time they stopped water cooling the machines (and coincidentally the CMOS got a lot less noise sensitive)
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals