#209148 - 03/10/13 10:28 AM Generator - emergency vs. standby
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Thinking out loud - A fairly large multi family with a standby generator for an elevator and some common area loads. Since we have it, we may as well put the exit lighting on the generator. Bt that means a separate transfer switch and distribution for the life safety loads (exit lighting). Do you think the elimination of a few dozen emergency battey pack lights is worth the added cost of the transfer switch, distribution, and associated generator up-grades?
Top
Work Gear for Electricians and the Trades
#209156 - 03/10/13 04:33 PM Re: Generator - emergency vs. standby [Re: cgw]
mbhydro Offline
Member
Registered: 02/21/03
Posts: 347
Loc: Winnipeg MB Canada
It depends if the upgrade costs are less than the ongoing costs of yearly battery light inspections (required by law here) and the eventual replacement of the battery packs when they go bad.
Top
#209159 - 03/10/13 04:43 PM Re: Generator - emergency vs. standby [Re: cgw]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
If the power goes out it's worth every penny. If it doesn't ...

What is the history of power outages, there?
Top
#209163 - 03/11/13 04:32 AM Re: Generator - emergency vs. standby [Re: cgw]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
In my experience any attempt to NOT use the backup gen-set 'blew up.'

BTW, there's no 'extra' switch required, at least not in my systems.

The critical loads are normally run through a sub-panel -- which is switched, entire, when Poco power drops out -- with, say, a seven second delay.

_________________________
Tesla
Top
#209169 - 03/12/13 07:57 AM Re: Generator - emergency vs. standby [Re: cgw]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
You will very likely need a separate ATS and panel depending on how your AHJ enforces the Code.
Emergency lighting and exit signage comes under Article 700 - Emergency Systems whereas elevators, security cameras and the like generally come under Article 702 - Optional Standby Loads.

The majority of the AHJs that I know will not allow you to mix those loads on a single ATS or a single panel.
_________________________
Ghost307
Top
#209181 - 03/13/13 06:18 PM Re: Generator - emergency vs. standby [Re: cgw]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Gentlemen:
I suggest that the OP start by reading the definitions within 700.2; 701.2; & 702.2 to clarify what may be the correct steps in addressing this subject.

Based on what the OP ststed, IMHO, the existing gen is not a 'Life Safety' power source, as again IMHO, the egress lighting is 'Life Safety' in a multi-family structure.

Also, keep in mind that different localities have different opinions and codes regarding life safety issues. The best place to start is your local AHJ, either Electrical, Building or Fire.
_________________________
John
Top
#210136 - 05/29/13 07:04 AM Re: Generator - emergency vs. standby [Re: cgw]
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
The space would required quite a few emergency (battery) lights. Normally I would eliminate the battery emergency lights and connect some of the building light fixtures to "emergency circuits". In this case however the distances of the emergency feeders would be significant. (100A feeder) about 200 ft from the generator to the transfer switch and another 400 ft to the other side of the building.
So instead of the emergency lights we would have:
600 feet feeder.
Two 100A panelboards.
100A transfer switch.
What ever the additional cost of the generator to make it emergency (instaed of just standby).
Top
#210137 - 05/29/13 07:37 AM Re: Generator - emergency vs. standby [Re: cgw]
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
Does this convert the unit definition from a standard standby unit to life a safety unit.
A life and safety unit here requires much more testing, annual certification and logging of maintenance records then a standard standby unit.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals