ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#209020 - 03/03/13 03:33 PM Receptacle in Dining room
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Okay, so here's my next question: Can a switched receptacle be on a small appliance branch circuit for dining room lighting?
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#209021 - 03/03/13 04:14 PM Re: Receptacle in Dining room [Re: George Little]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
IMO...no. 210.52(B)(2) says no other outlets can be on the small appliance branch circuits
Top
#209027 - 03/03/13 07:15 PM Re: Receptacle in Dining room [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Interesting question.

You need to have a luminaire, switched as your required lighting outlet to satisfy 210.70)A)(1)ex1 so who is to say that it is a lighting outlet if it was on one of two SA circuits?
210.52 tends to be contradictory. On the one hand they want 2 dedicated 20s serving the counter top, then they say you can pick up just about every other receptacle in the kitchen, dining room, pantry etc on those circuits.
The handbook does show a switched lighting outlet (receptacle) on a 15a general lighting circuit.
_________________________
Greg Fretwell
Top
#209030 - 03/04/13 06:18 AM Re: Receptacle in Dining room [Re: George Little]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Greg,

When I was in business, I would run about 3 different circuits to the kitchen. On one circuit, I would pick up 2-3 recpt. in kitchen and some in dining room. On another circuit, I would pick up 2-3 recpt. in kitchen then pick up some breakfast nook recpt. The last kitchen circuit would stay in the kitchen and they would have 3-4 recpt on it. Depending on the size of the kitchen.
Top
#209036 - 03/04/13 07:00 AM Re: Receptacle in Dining room [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I have seen some scary expensive houses that only had 2 for all of the required rooms. (kitchen, dining and a nook)

They also picked up 3 baths (counters) on one 20.

I was amazed at where some builders will save a buck.
_________________________
Greg Fretwell
Top
#209040 - 03/04/13 11:04 AM Re: Receptacle in Dining room [Re: George Little]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
I have to agree with Shortcircuit & say 'No', IF that circuit is one of the two required.

If it is an 'additional' 20 amp circuit then I feel it would be OK.

As to the bath receptacles all being on one circuit, compliant but a terrible design, and could be a major inconvenience for the occupants.
_________________________
John
Top
#209044 - 03/04/13 01:19 PM Re: Receptacle in Dining room [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I wonder if George's question comes down to whether a small appliance receptacle outlet can be switched? You already have the required lighting outlet.
_________________________
Greg Fretwell
Top
#209045 - 03/04/13 04:39 PM Re: Receptacle in Dining room [Re: George Little]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
I'm going to go with Greg, Short Circuit and Hot line's answers. One can not switch a receptacle on a 20a. SAC to satisfy the lighting outlet requirement mentioned in 210.70. It might be a stretch because the dining room is not mentioned in the exception but the wording in 210.52(B)(2) is pretty clear "No Other Outlets" meaning no lighting outlets. IMHO.
_________________________
George Little
Top
#209079 - 03/06/13 06:40 AM Re: Receptacle in Dining room [Re: George Little]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
George:
IF someone wanted 1/2 of a DR outlet switched for convenience, as in controling whatever was plugged into the 1/2, that would be compliant. (Using a 20 amp listed switch)

What say you?? Opinions appreciated.
_________________________
John
Top
#209081 - 03/06/13 06:45 AM Re: Receptacle in Dining room [Re: George Little]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
John,

I think I would have to pass that type of install if I saw it.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals