The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 66 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#208851 - 02/15/13 07:21 AM Wet loc or damp loc?
BigB Offline
Member

Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Is a shower ceiling considered a wet location or a damp location? Would a fan/fixture located in a shower ceiling have to show the rating in addition to stating that it is suitable for installation above a shower (along with GFCI requirements of course)?

Top
2017 / 2014 NEC & Related Books and Study Guides
#208852 - 02/15/13 09:24 AM Re: Wet loc or damp loc? [Re: BigB]
LEO_304E Offline
Member

Registered: 10/14/10
Posts: 17
Loc: MASSACHUSETTS
Originally Posted By BigB
Is a shower ceiling considered a wet location or a damp location? Would a fan/fixture located in a shower ceiling have to show the rating in addition to stating that it is suitable for installation above a shower (along with GFCI requirements of course)?
Yes ,It is a wet location.

I believe that all the fixtures rated for a shower area are also marked wet location.

Top
#208853 - 02/15/13 09:34 AM Re: Wet loc or damp loc? [Re: BigB]
LEO_304E Offline
Member

Registered: 10/14/10
Posts: 17
Loc: MASSACHUSETTS
Originally Posted By BigB
Is a shower ceiling considered a wet location or a damp location? Would a fan/fixture located in a shower ceiling have to show the rating in addition to stating that it is suitable for installation above a shower (along with GFCI requirements of course)?


Here is the 2011 NEC.

410.10 (D) Bathtub and Shower Areas. No parts of cord-connected
luminaires, chain-, cable-, or cord-suspended luminaires, lighting
track, pendants, or ceiling-suspended (paddle) fans shall
be located within a zone measured 900 mm (3 ft) horizontally
and 2.5 m (8 ft) vertically from the top of the bathtub rim or
shower stall threshold. This zone is all encompassing and includes
the space directly over the tub or shower stall. Luminaires
located within the actual outside dimension of the bathtub
or shower to a height of 2.5 m (8 ft) vertically from the top
of the bathtub rim or shower threshold shall be marked for
damp locations, or marked for wet locations where subject to
shower spray.



So the fixtures must be marked at least damp locations.

Top
#208855 - 02/15/13 11:13 AM Re: Wet loc or damp loc? [Re: BigB]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I am not sure where it says GFCI is required.

The handbook says "GFCI protection is required only where specified in the installation instructions for the luminaire."
_________________________
Greg Fretwell

Top
#208862 - 02/16/13 09:27 AM Re: Wet loc or damp loc? [Re: BigB]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Not unless the manufacture is requiring it? However if you have a very high ceiling above a shower stall, say 15 feet high, would that still be wet location? How about damp location?

Top
#208865 - 02/16/13 10:24 AM Re: Wet loc or damp loc? [Re: BigB]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Harold:
"Luminaires located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations where subject to shower spray."

To a height of 8' takes care of the tall ceilings. However, IF there is a chance the shower could spray up, then...all bets are off, and it's wet.

_________________________
John

Top
#208877 - 02/17/13 08:50 AM Re: Wet loc or damp loc? [Re: gfretwell]
Theelectrikid Offline
Member

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Originally Posted By gfretwell
I am not sure where it says GFCI is required.

The handbook says "GFCI protection is required only where specified in the installation instructions for the luminaire."


I know bath fans are typically rated for use right in the shower if they're downstream of a GFCI. Haven't seen a fixture for that otherwise since we usually do a hi-hat and shower trim.
_________________________
Is there anyone on board who knows how to fly a plane?

Top
#208891 - 02/18/13 08:44 PM Re: Wet loc or damp loc? [Re: BigB]
BigB Offline
Member

Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Yes I did mean GFCI by manufacturer requirements. Seems the "wet location if subject to shower spray" is a judgement call open for arguement, however it may be a moot point anyway as Leo said the fixtures rated for shower/tub area are all wet location fixtures anyway, and at least all the ones I could find were.

Top
#208949 - 02/23/13 10:25 AM Re: Wet loc or damp loc? [Re: BigB]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
John,

OK I agree if there is a chance of spray, then the light should be listed for a damp/wet location. However if you have a ceiling that is say, 15 feet above the shower, it is highly unlikely that if would be subject to water spray. Unless you let little kids with a bad snense of humor using a handheld shower head on "Stream" and shooting it straight in the air. Then in that case, the sink lights might also be subject to wet location, depending on the power of the handheld sprayer. smile

Top