The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by Potseal
47 minutes 15 seconds ago
Locked rotor, no burnout
by jraef
Today at 01:18 PM
Massive power outage South Australia
by Meadow
Today at 06:46 AM
short circuit??
by Meadow
Today at 06:43 AM
Norwegian power?
by Meadow
Today at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Potseal 7
Who's Online
2 registered (Trumpy, sparkyinak), 287 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#208139 - 12/29/12 12:36 PM Grounding Of Raceway
bossanova5 Offline
Member

Registered: 10/26/12
Posts: 13
Loc: L.A. CA
I'm installing overhead raceway for aproximately 50 machines in a machine shop.Most will be on 20 amp three pole breakers.I'm going to be running 2" EMT from the panel to the raceways.I'm thinking about running a #6 ground wire from the panel ground bar to the raceway,and installing(bonding) a terminal ground bar inside the raceway.From the ground bar in the raceway I would run a #12 ground wire to each machine saving me time and wire.I'm thinking this is legal

Any and all comments are appreciated.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#208141 - 12/29/12 01:08 PM Re: Grounding Of Raceway [Re: bossanova5]
bossanova5 Offline
Member

Registered: 10/26/12
Posts: 13
Loc: L.A. CA
I should add that I'll be running 1/2" emt from the raceway to each machine.

Top
#208142 - 12/29/12 01:12 PM Re: Grounding Of Raceway [Re: bossanova5]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Legally you could run a single #12 all the way to where you start splitting them out. The problem is the splice in the raceway. If there is adequate space, you can splice in a conduit body.
This is really a gray area since all grounding conductors only count as one.

You are also going to have some serious derating problems with that many conductors in a single raceway so we are not even talking about #12s. All of the wires, including the ground, have to start getting bigger when you go over three 3 phase circuits in a pipe. (9 current carrying THHN)
In the 10-20 wire range you will need #10.

At a certain point more raceways ends up being cheaper.
_________________________
Greg Fretwell

Top
#208146 - 12/29/12 04:46 PM Re: Grounding Of Raceway [Re: bossanova5]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6786
Loc: Brick, NJ USA
Bossanove5:

Heed these words...

"You are also going to have some serious derating problems with that many conductors in a single raceway so we are not even talking about #12s. All of the wires, including the ground, have to start getting bigger when you go over three 3 phase circuits in a pipe. (9 current carrying THHN)
In the 10-20 wire range you will need #10.

At a certain point more raceways ends up being cheaper."

I have seen what Greg is saying happen in the field a few times...results were downright ugly, expensive, and one cost a young guy an unwanted 'vacation.'

As to your question on the EGC...yes it is no issue to install a ground block within a wireway/troff/gutter and run a single EGC to the source panel. Common practice is to size the EGC from the panel to the block to the largest OCP of the circuits, although that is not an NEC requirement.
_________________________
John

Top
#208148 - 12/29/12 05:41 PM Re: Grounding Of Raceway [Re: bossanova5]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Quote:
within a raceway


Really?

How is that accessible? It is OK in a condolet tho.

Quote:
300.13 Mechanical and Electrical Continuity — Conductors.
(A) General. Conductors in raceways shall be continuous between outlets, boxes, devices, and so forth. There shall be no splice or tap within a raceway unless permitted by 300.15; 368.56(A); 376.56; 378.56; 384.56; 386.56; 388.56; or 390.6.


Each of those "unlesses" refers to a removable cover.
_________________________
Greg Fretwell

Top
#208152 - 12/29/12 07:27 PM Re: Grounding Of Raceway [Re: bossanova5]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6786
Loc: Brick, NJ USA
gREG:
i FEEL THAT THE op IS REFERING TO WIREWAY, TROFFS, NOT CONDUIT.
_________________________
John

Top
#208153 - 12/29/12 07:30 PM Re: Grounding Of Raceway [Re: bossanova5]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
OK my fault, I was confused by the 2" EMT thing.
_________________________
Greg Fretwell

Top
#208155 - 12/29/12 08:25 PM Re: Grounding Of Raceway [Re: bossanova5]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6786
Loc: Brick, NJ USA
Not as confused as my pittiful typing job above.!!!!!
_________________________
John

Top
#208156 - 12/29/12 08:31 PM Re: Grounding Of Raceway [Re: bossanova5]
bossanova5 Offline
Member

Registered: 10/26/12
Posts: 13
Loc: L.A. CA
Let me clear up the confusion:

The first 14 set of machines will have there own 6x6 square raceway.This raceway will be fed by a 2" conduit so the maximum #12 wires including the ground inside the raceway will equal 43 (Counting all the ground wires as one)

The second set of 19 machines will be fed the same way by (58 #12 wires) their own 6"x6" gutter and 2" pipe.

I know section 310.15(b)(a) calls for derating which permits only 10.5 amps for each #12 wire for the amount of wires I'm using.

The machines pull about 15.3 amps each.So I would have to use #8's which is kinda crazy.

Any more thoughts on this?

Thanks

Top
#208157 - 12/29/12 09:10 PM Re: Grounding Of Raceway [Re: bossanova5]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Just to be clear, grounds count as one for box fill but they are all counted in pipe. Again tho, you really only need one.

If you ran 3 raceways with the wires split up you would avoid the derating problem. Even 2 would be better, even if not legal.
_________________________
Greg Fretwell

Top