Recently I had an air handler shut down due to a wire rubbed where it goes into the motor. The wire rubbed and arced to ground where it went into the motor and the overload opened the circuit (this destroyed the overload, at 600 Volt!!!) The surprise to me was the fact that the wires are three hots and a bond tie wrapped to the frame of the air handler from the starter/overloads to the motor. Not teck or BX but just three hots and a bond. There are six other air handlers that are wired the same way. The motors have an anti short put into the motor where a connector would thread in. The air handlers are electically certified for Canada but this does not seem proper. Shouldn't these wire be ran in armour or sheathing with proper connectors or???? This particular motor that arced had no anti short installed.
Top
Tools for Electricians:
#207997 - 12/16/12 06:55 PM Re: R90 in air handling unit [Re: wacked]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
That's the way roof top units and furnaces are, too.
Top
#208007 - 12/17/12 02:59 PM Re: R90 in air handling unit [Re: wacked]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Wacked.
How the unit is wired is a function of the product approval standard for air handling equipment. This is Part 2 OF the Canadian Electrical code. This is why an inspector looks for an approval label to verify the thing was made to the OTHER electrical code. Ther is a part 3 , 4 and 5 too.

Your work as an electrician is the installation of electrical products which is PART 1 of the CEC and the portion of the code electricians break and inspectors reject or approve.

How the product is wired intenally is not governed by your part 1 installation code. It is regulated by Part 2 which is a lot of code books that govern how the product is made and how it performs as well as the market it is approved for like household and commercial.

Just like the wiring for your range is open inside the stove so may be some of the wiring inside your AH unit.
Top
#208093 - 12/24/12 06:03 PM Re: R90 in air handling unit [Re: wacked]
wacked Offline
Member
Registered: 12/19/06
Posts: 33
This unit does have an approval label... that still doesn't make it proper due to the fact that there was a failure.
I have looked at other air handlers and teck is used more often than not. Maybe the "other code" for packaged units need to be reviewed.
Top
#208322 - 01/11/13 12:01 PM Re: R90 in air handling unit [Re: wacked]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
You are saying a manufacturer like engineered air is using teck internally to wire the motors? I don't see that. I built this stuff briefly in an earlier life and we did not use tech or acwu internal wiring. Sometimes we used seal tight. it is very common to see what you describe inside of these air units. The fault is a manufacturers error and I would report that to the Certification Body that approved it. I.E. CSA or cUL. We regulary report product defects to them as they can make the manufacturer fiz the wiring methods used internally.
You cannot judge how a piece of approved equipment is internally wired by comparing it to the code book methods. The code book is about how we wire the parts together the other part of the coed is how the factory makes the products we wire.
Your description of how various factories wire the motors is more related to their designs and what is more important to them withing the part 2 standards.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals