#207932 - 12/09/12 04:10 PM Fluorescent Lighting calculations
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
I must be getting old!! I connot seem to remember how to find the wattage of a fluorescent fixture. 2 f40's with a magnetic ballast? I think .51 for the ballast.


Ob
_________________________
Choose your customers, don't let them choose you.
Top
Work Gear for Electricians and the Trades
#207939 - 12/09/12 08:08 PM Re: Fluorescent Lighting calculations [Re: Obsaleet]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
It is based on tha ballast rating. If the fixture info is in front of me, I go to manufacters website and find a similar ballast and pad my numbers to be on the safe side
_________________________
"Live Awesome!" - Kevin Carosa
Top
#207941 - 12/10/12 12:01 AM Re: Fluorescent Lighting calculations [Re: Obsaleet]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I think there is some safety margin built into that "40w".
When I put my clamp on a shop lite fixture with to F40CWs in it I actually get less than 80w, ballast and all.

Someone point out it might just be the meter is not handling the wave form properly tho.
_________________________
Greg Fretwell
Top
#207942 - 12/10/12 01:10 AM Re: Fluorescent Lighting calculations [Re: gfretwell]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
According to the GE Lighting Institute, the watt rating of the bulbs has nothing to do with the draw of the fixture. Hence, use the ballast rating


Edited by sparkyinak (12/10/12 01:11 AM)
_________________________
"Live Awesome!" - Kevin Carosa
Top
#207992 - 12/16/12 11:15 AM Re: Fluorescent Lighting calculations [Re: Obsaleet]
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
This is why I am confused. I thought that you add the ballast to the lamps and thats your total. Then I googled just to see and found so many different ways and none ended with the same result.
_________________________
Choose your customers, don't let them choose you.
Top
#207993 - 12/16/12 12:40 PM Re: Fluorescent Lighting calculations [Re: Obsaleet]
HTSR77 Offline
New Member
Registered: 12/06/12
Posts: 2
Loc: Washington
I agree with SparkinAK. When determining the size of the connected load or branch circuit for lighting, the ballast input in watts is used.
Top
#207998 - 12/16/12 08:33 PM Re: Fluorescent Lighting calculations [Re: Obsaleet]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Ballast data is used for actual lighting connected load calcs. Using the bulb wattage (2x40, 4x32,) can be used for a 'ballpark' figurre, which will be higher most of the time, than actual.

The same applies for HID lighting, use ballast data, not bulb wattage.
_________________________
John
Top
#208000 - 12/17/12 03:17 AM Re: Fluorescent Lighting calculations [Re: HotLine1]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
Normally I use the ballast data to sized the circuit and I don't bother to read the lamp wattage but useally resvered for ballpark figures plus add about 20% or so so you should land right on the spot.

Merci,
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#208108 - 12/27/12 02:33 AM Re: Fluorescent Lighting calculations [Re: Obsaleet]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
I agree with the previously posts - use the Ballast Data.

BTW, A Magnetic Rapid Start Ballast Load for Driving (2) F40T12 Lamps would be:

Line Input - 120 VAC:
Line Amperes = 0.69A
ANSI Watts = 82W
Average Ballast Factor = 0.84
BEF (Eff. Factor) = 1.02

Line Input - 277 VAC:
Line Amperes = 0.33A
ANSI Watts = 90W
Average Ballast Factor = 0.87
BEF (Eff. Factor) = 1.04

BTW, these figures are for F40T12 Lamps driven with the Cathodes being constantly Heated - AKA Rapid Start / Hot Cathode Operation.
Values will be lower for Instant Start Ballasting.
For Programmed Start Ballasting, the initial or Maximum Values will be similar.

Lamps will almost always draw less Wattage than they are rated at - especially when operated in extremely Cold or Warm environments.

--Scott (EE)
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals