The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
gfretwell 13
ghost307 12
Who's Online
0 registered (), 0 Guests and 179 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#207331 - 10/17/12 02:07 PM US ELECTRICS
ANNEMARIE Offline
Member

Registered: 10/11/12
Posts: 41
Loc: DORSET UK
Hi i am curious if a workshop in the us has a 277/480 volt supply is the 120 volt supply for office and other equipment derived from a seperate pole xformer or from a xformer in the building thanks from annemarie

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#207332 - 10/17/12 02:41 PM Re: US ELECTRICS [Re: ANNEMARIE]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6831
Loc: Brick, NJ USA
Usual practice is a customer owned transformer to step down 480 to 120/208 volt.

There are instances where there are multiple utility services with different voltage characteristics, but the most common are customer owned transformers

_________________________
John

Top
#207343 - 10/18/12 10:37 AM Re: US ELECTRICS [Re: ANNEMARIE]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Annemarie, I have installed the electrical systems for a number of commercial and light industrial buildings.

The usual method is for the power company to provice 480 volt "three phase" power, with a neutral - so it's 277v. from any 'hot' wire to the neutral, and 480v between any two 'hot' lines.

A customer-owned ('customer' being the building owner, and not the tenant paying the electric bill) transformer will be installed to supply a panel with 208v/120v three phase power.

Any line-to-neutral circuit is single phase.

Often there will be a 480v panel set next to the 208v panel. 277v circuits are often drawn from the 480v panel for the permanent lighting. Most of your machine loads will also come from the 480v panel.

The 208/120 panel is usually filled with just 120v circuits. An exception might be the air conditioning; those guys never order the right (480v) stuff.

This is the usual, and preferred, practice. There are plenty of exceptions, usually found in older areas.


Top
#207345 - 10/18/12 01:21 PM Re: US ELECTRICS [Re: renosteinke]
ANNEMARIE Offline
Member

Registered: 10/11/12
Posts: 41
Loc: DORSET UK
Thanks for your reply they are both very informative im glad i found this site thanks all Annemarie

Top
#207355 - 10/19/12 07:49 AM Re: US ELECTRICS [Re: ANNEMARIE]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
And just for reference in Canada we usually use 600/347 instead of 480/277 volts.