#207331 - 10/17/12 02:07 PM US ELECTRICS
ANNEMARIE Offline
Member
Registered: 10/11/12
Posts: 39
Loc: DORSET UK
Hi i am curious if a workshop in the us has a 277/480 volt supply is the 120 volt supply for office and other equipment derived from a seperate pole xformer or from a xformer in the building thanks from annemarie
Top
Work Gear for Electricians and the Trades
#207332 - 10/17/12 02:41 PM Re: US ELECTRICS [Re: ANNEMARIE]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Usual practice is a customer owned transformer to step down 480 to 120/208 volt.

There are instances where there are multiple utility services with different voltage characteristics, but the most common are customer owned transformers

_________________________
John
Top
#207343 - 10/18/12 10:37 AM Re: US ELECTRICS [Re: ANNEMARIE]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Annemarie, I have installed the electrical systems for a number of commercial and light industrial buildings.

The usual method is for the power company to provice 480 volt "three phase" power, with a neutral - so it's 277v. from any 'hot' wire to the neutral, and 480v between any two 'hot' lines.

A customer-owned ('customer' being the building owner, and not the tenant paying the electric bill) transformer will be installed to supply a panel with 208v/120v three phase power.

Any line-to-neutral circuit is single phase.

Often there will be a 480v panel set next to the 208v panel. 277v circuits are often drawn from the 480v panel for the permanent lighting. Most of your machine loads will also come from the 480v panel.

The 208/120 panel is usually filled with just 120v circuits. An exception might be the air conditioning; those guys never order the right (480v) stuff.

This is the usual, and preferred, practice. There are plenty of exceptions, usually found in older areas.

Top
#207345 - 10/18/12 01:21 PM Re: US ELECTRICS [Re: renosteinke]
ANNEMARIE Offline
Member
Registered: 10/11/12
Posts: 39
Loc: DORSET UK
Thanks for your reply they are both very informative im glad i found this site thanks all Annemarie
Top
#207355 - 10/19/12 07:49 AM Re: US ELECTRICS [Re: ANNEMARIE]
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
And just for reference in Canada we usually use 600/347 instead of 480/277 volts.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals