#206953 - 09/07/12 06:48 AM Underground Feeders to fire pump
beatricellc Offline
New Member
Registered: 07/19/12
Posts: 6
Loc: cook county, IL
In a Chicago high rise, feeders to a fire pump are below the floor of a parking garage. Fire pump controller is from around 1959. 480V 3 phase/ 150hp.

About 250' from the meter, there is a junction box in the floor. It is about another 100' to the fire pump. There is 3" conduit, and fiber bushings, at opposite ends of the rectangle shaped box. The box is falling apart. The conduit end, at the fire pump side of the box, is collapsing and closing in on the wire. There are 3 feeders. The insulation from one of the feeders is not cut but is "bulging" from the squeeze.

If after I megger the wire and find it to be OK. Can I just repair the damaged feeder? Is it acceptable to "sleeve" the damaged conduit end with an insulator?
Top
2017 / 2014 NEC & Related Books and Study Guides
#206954 - 09/07/12 07:24 AM Re: Underground Feeders to fire pump [Re: beatricellc]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA

That answer is best for you IF it comes from the local AHJs.
_________________________
John
Top
#206955 - 09/07/12 09:35 AM Re: Underground Feeders to fire pump [Re: beatricellc]
beatricellc Offline
New Member
Registered: 07/19/12
Posts: 6
Loc: cook county, IL
What is an AHJ?
Top
#206956 - 09/07/12 09:48 AM Re: Underground Feeders to fire pump [Re: beatricellc]
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
Authority Having Jurisdiction. Inspectors.
Top
#206957 - 09/07/12 11:08 AM Re: Underground Feeders to fire pump [Re: beatricellc]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I agree with John. Get your local electrical inspector in there, show him the problem and see what you can work out.

From the sound of it, you might be chipping up some floor. These days with diamond saws and air tools, it is usually not that big a deal. You might be meeting a guy from the concrete worker's union tho (in Chicago).

Once you get it opened up you should be able to get back to clean pipe and extend it a little, into your new enclosure or just use a bigger box.
_________________________
Greg Fretwell
Top
#206958 - 09/07/12 03:54 PM Re: Underground Feeders to fire pump [Re: beatricellc]
beatricellc Offline
New Member
Registered: 07/19/12
Posts: 6
Loc: cook county, IL
Thanks. I was looking into cutting the floor and a new box as the next option.
Top
#206959 - 09/07/12 05:34 PM Re: Underground Feeders to fire pump [Re: beatricellc]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
The point of where I was going with a suggestion is that you should have a talk with the electrical inspector, and possibly the fire inspector before you plan any repairs.

Discussion regarding what is acceptable, and providing details (sketch) is a lot easier than doing something & not having it approved.
_________________________
John
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals