#206916 - 09/01/12 01:31 AM Meter & load center proximity to pool  
BigB  Offline
Member
Joined: Mar 2004
Posts: 719
Tucson, AZ USA
There is a concern on an existing installation where the meter and outdoor load center are approximately 7 feet from the inside wall of an in ground pool. Looking thru 680 I see no violation, not even a requirement to include it in the equipotential bonding as it is not within 5 feet of the inside wall. Am I correct?


2017 / 2014 NEC & Related Books and Study Guides

#206918 - 09/01/12 01:04 PM Re: Meter & load center proximity to pool [Re: BigB]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
I think you are right but look up. Where is the service drop?


Greg Fretwell

#206919 - 09/01/12 03:59 PM Re: Meter & load center proximity to pool [Re: gfretwell]  
BigB  Offline
Member
Joined: Mar 2004
Posts: 719
Tucson, AZ USA
Originally Posted by gfretwell
I think you are right but look up. Where is the service drop?


The service conductors are piped across the roof for 25 feet then there is a 90 up with a weatherhead. Adjacent to this weatherhead there is a service mast fastened to the building to support the overhead, keeping it 25' from the water. It is not pretty.


#206920 - 09/01/12 05:25 PM Re: Meter & load center proximity to pool [Re: BigB]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
It sounds legal tho... sometimes the law ain't pretty wink

Was any consideration given to raceways on a roof? (derating)


Greg Fretwell

#206924 - 09/01/12 10:37 PM Re: Meter & load center proximity to pool [Re: gfretwell]  
BigB  Offline
Member
Joined: Mar 2004
Posts: 719
Tucson, AZ USA
Originally Posted by gfretwell
It sounds legal tho... sometimes the law ain't pretty wink

Was any consideration given to raceways on a roof? (derating)


I doubt it since my area just started enforcing derating for ambient last year, and this installation is at least 30 years old. This brings up something I have been wondering about, when de-rating residential service conductors would you start with the ampacities listed in table 310.15(B)(6)?


#206930 - 09/02/12 12:51 PM Re: Meter & load center proximity to pool [Re: BigB]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
That is why I was curious.
310.15(B)(2)(c) refers you to 310.16
I am not sure what you do with (B)(6) service feeders. I was wondering what size they ended up with.


Greg Fretwell


Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,428
Joined: February 2004
Show All Member Profiles 