#206734 - 08/04/12 09:26 AM Bond bushings
SJT Offline
Member
Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
In regard to threaded grounding bushings (with grounding lug on it), where are these to be installed?
I was checking 250.97 and 300.4(G) in the code.
If possible, could you refer me to the code sections, where we must install such bushings, as compared to normal bushings?
Just trying to have code references, so we don't install ground bushings where they are not needed.
Thanks - Good day
SJT
Top
2017 / 2014 NEC & Related Books and Study Guides
#206739 - 08/04/12 07:54 PM Re: Bond bushings [Re: SJT]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
The SINGLE most common use for such grounding bushings is at the terminus of an EMT, GRC, IMC, Flex shielded run on a GEC -- wherever its headed.

Sometimes I've installed them as a grounding lug even with a naked bare GEC system bonding conductor.

Other than that, they've got little purpose.

They are never used to replace lazy-lugs/ lay-in lugs.

And they are typically UL listed for conductor size -- maxxed at 3/0 -- the largest GEC from the table.

That's one hint from the manufacturer/ UL as to their purpose -- they're choke eliminators -- and the inspector will be looking for them on all GEC bonding runs that are wrapped in steel pipe/ steel flex.

They are NOT required if the same run is wrapped in PVC.

As for GEC Systems, the NEC Handbook has sweet illustrations. Exhibit 250.32 [ BTW, the bushing is normally attached physically to the raceway -- but it doesn't absolutely have to -- see the diagram.

NEC 250.64.E

NEC 250.104

Happy to post the citations for the forum...

(2005 copy...)
_________________________
Tesla
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 79 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals