What is a typical required light level specified for temporary general construction lighting? I have seen 50FC specified but that seems really high and had to achieve.
Top
Work Gear for Electricians and the Trades
#206728 - 08/03/12 09:46 AM Re: Temporary Construction Lighting [Re: cgw]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You are 5x to 10x the real rule, depending on what kind of "construction area"

it is 5 FC in general construction areas, 10 FC in batch plants and electrical equipment rooms but as low as 3 FC if you are excavating, placing concrete or storing materials

http://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=STANDARDS&p_id=10630

50 FC would be a very brightly lit office.
_________________________
Greg Fretwell
Top
#206747 - 08/06/12 09:02 AM Re: Temporary Construction Lighting [Re: cgw]
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Thanks
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 70 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals