The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 245 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#206680 - 07/31/12 09:49 AM Article 200.4
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I don't have my code book handy but am reading from a print out of major changes in the 2011 code. It says, "Will not allow a neutral conductor to be used for more than one branch circuit or feeder". Does this mean no more shared neutrals on 14/3 or 12/3 ? thanks..

Top
2014 / 2011 NEC & Related Books and Study Guides
#206681 - 07/31/12 11:11 AM Re: Article 200.4 [Re: sparkync]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
sparkync:

The rest of that sentence answers your question....

Neutral conductors shall not be used for more than one branch circuit, for more than one multiwire branch circuit, or for more than one set of ungrounded feeder conductors unless specifically permitted elseware within this Code.

from the '11 NEC Handbook; NOT commentary, Code text.
_________________________
John

Top
#206682 - 07/31/12 01:58 PM Re: Article 200.4 [Re: HotLine1]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Guess I just need to go and get my code book and read frown

Thanks a lot, Steve...

Top
#206686 - 07/31/12 02:15 PM Re: Article 200.4 [Re: sparkync]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The short answer is a multiwire circuit is ONE circuit. That can be 2 ungrounded conductors in 120/240 or 3 ungrounded conductors in 208 wye.
There are requirements about how and where these conductors have to be grouped and how overcurrent devices are coordinated (getting tougher each cycle it seems) but it is still one circuit.
_________________________
Greg Fretwell

Top
#206712 - 08/02/12 01:58 PM Re: Article 200.4 [Re: sparkync]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Greg, that being said, when did the code every allow a neutral to serve more than one branch circuit except with a feeder that is feeding another panel?


Edited by sparkync (08/02/12 01:59 PM)

Top
#206716 - 08/02/12 03:02 PM Re: Article 200.4 [Re: sparkync]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I believe the only way a neutral can feed more than one circuit is if it is in a feeder. The code has been that way as long as I can remember.
_________________________
Greg Fretwell

Top
#206718 - 08/02/12 04:34 PM Re: Article 200.4 [Re: sparkync]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
I have to agree with Greg. Strolling down memory lane, nothing jumps out at me. Time permitting, I may crack open the oldest NEC in my collection.
_________________________
John

Top
#206727 - 08/03/12 09:27 AM Re: Article 200.4 [Re: sparkync]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
This discussion reminds me of one of my 'creative' moments. I was under the impression that the new code language made my otherwise legal solution forbidden.

It was a small house, a complete rewire. Construction was solid masonry. Fortunately, there was an attic.

Even so, the large EMT (not sure of the size)I ran out the side of the outside panel, up the wall, and into the attic was pretty tight. So, to reduce my wire fill, I placed a can in the attic and mounted some terminal strips. I landed my grounds on one strip, and my neutrals on another. I did run a #10 ground wire (redundant to the conduit) and, I believe, a #6 neutral (the largest circuit was 20-amp, and circuits were split between legs) from the can to the panel. Thus, that pipe had many 'hot' wires, but only one ground and one neutral.

It was an exceptional situation, and I have not used this method again. Under the current code, I am clearly not allowed to do this.