The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#206409 - 06/29/12 11:39 AM 600V single phase 2-wire
Napo Offline
New Member
Registered: 06/29/12
Posts: 1
Loc: Alberta
If you are running a 50mm DB2 underground conduit, for a 2-wire, single phase 600V system (no neutral) between two lighting panels (which have a 600V to 120V transformer) is it mandatory to run a third wire as bonding conductor(to ground)?

The panel themselves have their own grounding electrodes.
The 600V circuits are #2Cu, so in general the code would call for a #6 bonding conductor.

What is the CEC rule/subrule that would make the bonding conductor mandatory? I am not sure I read 10-106 properly.
Top
Tools for Electricians:
#206410 - 06/29/12 12:07 PM Re: 600V single phase 2-wire [Re: Napo]
mikesh Offline
Member
Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
You do have to install a bonding wire with the 600 volt wires so if a fault occurs on the primary side that the upstream breaker can trip. The secondary side has a new ground and bonding jumper to serve the 120 volt side.
There are some cases where you can save on the bonding wire but not this case.
When you feed an out building and create a new service entry the neutral can act as the bonding and as the grounded circuit conductor but because the 2 systems are electrically isolated the 600 volt side needs a bonding wire to return fault current to its source but not for the secondary which works like a new service.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (sparkyinak), 108 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals