#206402 - 06/28/12 08:16 PM Pool wiring
harold endean Offline
Member
Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Is an aluminum lug mounted on a pool heater allowed by the NEC?
Top
Work Gear for Electricians and the Trades
#206404 - 06/29/12 06:29 AM Re: Pool wiring [Re: harold endean]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Harold:

Dissimilar metals? 110.3(b) issue? Not suitable for the enviornment?

I had an issue with lugs used on a large solar panel project here, similar to what I think you are getting at. It took documentation from the lug mfg (OEM) to determine that that particular lug was NOT UL approved for exterior, exposed to the elements.

_________________________
John
Top
#206419 - 07/01/12 08:29 AM Re: Pool wiring [Re: harold endean]
mikethebull Offline
Member
Registered: 03/18/07
Posts: 101
Loc: Rhode Island
Also 110.14 Electrical Connections. And 680.9 says loads subdived not to exceed 48 amps & protected not over 60 amps...
Top
#206424 - 07/01/12 10:22 AM Re: Pool wiring [Re: harold endean]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
John,

I was talking to Susanne on Friday and she also quoted 110.14 as did Mike. I have been failing AL lugs on pool heaters since becoming an AHJ 14 years ago. I called up a leading manufacture of pool equipment and asked them why they put AL lugs on pool heaters when it isn't allowed by the NEC. Their only response to me was that U* (You might be able to guess the letter) allows them to do it. I also called U* and asked them about it and asked them why they list the units with AL and they said that they would have to get back to me. That was 14 years ago and I am still waiting for that call back. smile
Top
#206426 - 07/01/12 05:24 PM Re: Pool wiring [Re: harold endean]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Harold:
Based on your above post did Susan say 'NO, the alum lugs cannot be used'??

Did the manufacturer allude that the heater WITH the Al lug was a fully listed assembly. or were they saying the Al lug is 'listed'??

110.14 Electrical Connections. Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.

Connectors and terminals for conductors more finely
stranded than Class B and Class C stranding as shown in
Chapter 9, Table 10, shall be identified for the specific
conductor class or classes.
_________________________
John
Top
#206481 - 07/07/12 01:22 PM Re: Pool wiring [Re: harold endean]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Harold, send a note to Jeff and ask him about it.

Jeffrey.Fecteau@ul.com
_________________________
Greg Fretwell
Top
#206487 - 07/09/12 06:33 AM Re: Pool wiring [Re: harold endean]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
John,

She said that the Al lug can fail inspection because of sec. 110.14 of the NEC as you have stated above.
Top
#206488 - 07/09/12 06:35 AM Re: Pool wiring [Re: harold endean]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Greg,

I will try to shoot off an e-mail today if I get the chance.

However the DCA of NJ stated that the pool manufacture has been told to remove the AL lugs and that they will tell them again.
Top
#206490 - 07/09/12 06:37 AM Re: Pool wiring [Re: harold endean]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
While I am here, does anyone know if the pool widget is UL approved for above ground pool bonding?

The pool widget is a short (nipple?)piece of metal that goes on the pool skimmer hose and has a regular bonding clamp on it. From the looks of the picture, the clamp looks like it is suitable for direct burial.
Top
#206491 - 07/09/12 06:47 AM Re: Pool wiring [Re: harold endean]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Harold:
The ones I have seen are UL marked. The lug appears to have 'DB' stamped.
_________________________
John
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 72 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals