Hello,
Can someone direct me to the NEC section regarding sleeveing romex in conduit for a combination of 12/2 and 14/2, over 10'
thanks,
Joe
Top
2017 / 2014 NEC & Related Books and Study Guides
#206307 - 06/15/12 09:14 AM Re: type NM in conduit [Re: jkraft]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
334.15(B)
Quote:
Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means extending at least 150 mm (6 in.) above the floor.


Note 9 to table 9 (conduit fill) says
Quote:
(9)A multiconductor cable or flexible cord of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that have elliptical cross sections, the cross-sectional area calculation shall be based on using the major diameter of the ellipse as a circle diameter.


two cables can't be stacked and measured, You have to compute for "2 conductors" the size of the widest dimension so you end up with some pretty big pipe.
I haven't run the numbers on a 12 and a 14 but 1" would not surprise me
_________________________
Greg Fretwell
Top
#206308 - 06/15/12 09:41 AM Re: type NM in conduit [Re: gfretwell]
jkraft Offline
Member
Registered: 05/05/03
Posts: 74
thanks for your help Greg, looking at those sections now and trying to determine what size IMC would be needed for 1-12/2 and 2-14/2???
Top
#206309 - 06/15/12 11:03 AM Re: type NM in conduit [Re: jkraft]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
OK lets run the numbers
I will use commie metric because I prefer decimals

The 14ga I have measures 9mm, 12ga measures 10mm (across the widest part.

The area is the radius (half the diameter above)squared times pi (3.14)

5 x 5 x 3.14 = 78.5 mm2
4.5 x 4.5 x 3.14 = 63.6 mm2
Total cable area = 142.1 mm2

Take that to table 9 IMC "2 wire" column and you end up with 1" IMC (up to 192 mm2)
3/4 only gives you 117 mm2

See why I wasn't surprised? wink

_________________________
Greg Fretwell
Top
#206316 - 06/15/12 06:59 PM Re: type NM in conduit [Re: jkraft]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Nice answer Greg. Not everyone knows about this approach. Most contractors want to skin the outer jacket from the NM cable and not worry about the rules. A clear violation of 312.5(C)(e).


Edited by George Little (06/15/12 07:12 PM)
_________________________
George Little
Top
#206317 - 06/15/12 08:27 PM Re: type NM in conduit [Re: jkraft]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Greg:
Ditto with what George said! Nice!!
_________________________
John
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals