#206304 - 06/15/12 08:27 AM type NM in conduit
jkraft Offline
Member
Registered: 05/05/03
Posts: 75
Hello,
Can someone direct me to the NEC section regarding sleeveing romex in conduit for a combination of 12/2 and 14/2, over 10'
thanks,
Joe
Top
2017 / 2014 NEC & Related Books and Study Guides
#206307 - 06/15/12 09:14 AM Re: type NM in conduit [Re: jkraft]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
334.15(B)
Quote:
Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means extending at least 150 mm (6 in.) above the floor.


Note 9 to table 9 (conduit fill) says
Quote:
(9)A multiconductor cable or flexible cord of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that have elliptical cross sections, the cross-sectional area calculation shall be based on using the major diameter of the ellipse as a circle diameter.


two cables can't be stacked and measured, You have to compute for "2 conductors" the size of the widest dimension so you end up with some pretty big pipe.
I haven't run the numbers on a 12 and a 14 but 1" would not surprise me
_________________________
Greg Fretwell
Top
#206308 - 06/15/12 09:41 AM Re: type NM in conduit [Re: gfretwell]
jkraft Offline
Member
Registered: 05/05/03
Posts: 75
thanks for your help Greg, looking at those sections now and trying to determine what size IMC would be needed for 1-12/2 and 2-14/2???
Top
#206309 - 06/15/12 11:03 AM Re: type NM in conduit [Re: jkraft]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
OK lets run the numbers
I will use commie metric because I prefer decimals

The 14ga I have measures 9mm, 12ga measures 10mm (across the widest part.

The area is the radius (half the diameter above)squared times pi (3.14)

5 x 5 x 3.14 = 78.5 mm2
4.5 x 4.5 x 3.14 = 63.6 mm2
Total cable area = 142.1 mm2

Take that to table 9 IMC "2 wire" column and you end up with 1" IMC (up to 192 mm2)
3/4 only gives you 117 mm2

See why I wasn't surprised? wink

_________________________
Greg Fretwell
Top
#206316 - 06/15/12 06:59 PM Re: type NM in conduit [Re: jkraft]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Nice answer Greg. Not everyone knows about this approach. Most contractors want to skin the outer jacket from the NM cable and not worry about the rules. A clear violation of 312.5(C)(e).


Edited by George Little (06/15/12 07:12 PM)
_________________________
George Little
Top
#206317 - 06/15/12 08:27 PM Re: type NM in conduit [Re: jkraft]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Greg:
Ditto with what George said! Nice!!
_________________________
John
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 59 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals