The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 178 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#206250 - 06/10/12 10:04 PM electric furnace
homerjones Offline
Member

Registered: 12/08/07
Posts: 34
Loc: 0nt.
i have a 15 kw electric furnace, i want to install in my house. i temporarily used 2conducter 2 with a 100 amp breaker. i need to move the furnace to a different location in the basement to accomadate a/c and i want to run conduit to make it neater. the unit draws 60 amps even though the nameplate says 64. i don't have a current codebook but i was hoping to run 2 number 4s in a 1 inch conduit and still have to use the 100 amp breaker. help me out with this one please?

Top
2017 / 2014 NEC & Related Books and Study Guides
#206251 - 06/10/12 10:48 PM Re: electric furnace [Re: homerjones]
homerjones Offline
Member

Registered: 12/08/07
Posts: 34
Loc: 0nt.
forgot to add im in ontario as that can make a big difference in rules.