The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 175 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#206216 - 06/07/12 05:03 PM Gas dryer outlet on with laundry circuit??
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Can a 120 volt outlet for the dryer be put on with the 20 amp. laundry circuit?? Thanks, Steve..

Top
2014 / 2011 NEC & Related Books and Study Guides
#206217 - 06/07/12 05:48 PM Re: Gas dryer outlet on with laundry circuit?? [Re: sparkync]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Yes sir!
_________________________
John

Top
#206222 - 06/07/12 06:41 PM Re: Gas dryer outlet on with laundry circuit?? [Re: sparkync]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Thanks John, that's what I thought. Just wanted to make sure.

Top
#206224 - 06/07/12 07:19 PM Re: Gas dryer outlet on with laundry circuit?? [Re: sparkync]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Yup there is some confusion about this. You are really just required to provide a 20a circuit for the "laundry". There is no restriction about how many receptacles can be on that circuit or what you can plug into as long as it is in the laundry.When I see a single 20 behind the washer location I understand someone has misunderstood where we are supposed to be going with this. They want you to be able to run the washer and the iron at the same time.
Kids there used to be this thing called an iron ... wink
_________________________
Greg Fretwell

Top
#206225 - 06/07/12 07:34 PM Re: Gas dryer outlet on with laundry circuit?? [Re: sparkync]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Hey Greg- You old timer, can I put my mangle on the laundry circuit? :))


Here's my real questionó If I have a 120/240v. staked unit, do I still have to put in a 20a. 120v. laundry circuit?


Just jerking your chain Greg.
_________________________
George Little

Top
#206226 - 06/07/12 07:37 PM Re: Gas dryer outlet on with laundry circuit?? [Re: sparkync]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Yes!!
_________________________
John

Top
#206228 - 06/07/12 08:22 PM Re: Gas dryer outlet on with laundry circuit?? [Re: sparkync]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
George
Do you mean one of these? Just serving the laundry?

I am not sure what I would cite to require an additional circuit.




Quote:
210.11(C)(2) Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.


It doesn't say 120v only
_________________________
Greg Fretwell

Top
#206230 - 06/07/12 09:28 PM Re: Gas dryer outlet on with laundry circuit?? [Re: sparkync]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Greg, I'm not sure of the amperage on the stacked unit but I was thinking it was 30a. Haven't seen one in a while. With that in mind, if it were 30a. the question becomes do you still need a 20a. circuit for the iron? or for some of us folks the Mangle. I think the Stacked unit is a 30a. 240v. single receptacle.
_________________________
George Little

Top
#206231 - 06/07/12 10:02 PM Re: Gas dryer outlet on with laundry circuit?? [Re: sparkync]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You still need a 120v 20a circuit.

I was confused by the "stacked" question. I see now you mean a stack washer/dryer.
_________________________
Greg Fretwell

Top