#206157 - 05/30/12 07:33 AM bonding or grounding question
sidmuer Offline
Member
Registered: 05/01/12
Posts: 13
Loc: Ontario
Hello,
If I have a 60 AMP panel or device on 60 AMP breaker, and the wires are 2/0 RW90XLPE feeding the panel or device, do I size the ground for panel or bond for device by the wire size or by the panel rating/breaker size or, if it's a device, by the breaker size of that device?

I know for a panel, min size for ground is #6. So for the 60 AMP panel, I'd need at least that. But that is still well below the size needed to ground 2/0 rated wire.
Or a bond for 2/0 rated wire running from a 60 AMP breaker to a device.

I just don't know if I am supposed to size grounding or bonding by the size of wire ran or the breaker it is on. I would hope by the breaker size.
Top
Tools for Electricians:
#206176 - 05/31/12 07:30 AM Re: bonding or grounding question [Re: sidmuer]
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
If you use table 16 it is based on the 'largest ungrounded conductor in the circuit..." not on the panel size or overcurrent protection.


Edited by jdevlin (05/31/12 07:30 AM)
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (Admin), 60 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals