ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 263 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
Hello,
If I have a 60 AMP panel or device on 60 AMP breaker, and the wires are 2/0 RW90XLPE feeding the panel or device, do I size the ground for panel or bond for device by the wire size or by the panel rating/breaker size or, if it's a device, by the breaker size of that device?

I know for a panel, min size for ground is #6. So for the 60 AMP panel, I'd need at least that. But that is still well below the size needed to ground 2/0 rated wire.
Or a bond for 2/0 rated wire running from a 60 AMP breaker to a device.

I just don't know if I am supposed to size grounding or bonding by the size of wire ran or the breaker it is on. I would hope by the breaker size.

Joined: Aug 2002
Posts: 402
J
Member
If you use table 16 it is based on the 'largest ungrounded conductor in the circuit..." not on the panel size or overcurrent protection.