The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 295 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#206032 - 05/12/12 08:58 PM disconnect for gate operator
schenimann Offline
Member

Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
A local homeowners association is wanting to put disconnects on their pad mounted gate operator. I am not sure if it is 110v or 220v. They are wanting to disconnect the standard voltage as well as the battery backup. Is the best way to mount a post on the pad and put the disconnects on this? Can I use toggles rated for the proper voltage? Thanks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#206033 - 05/12/12 09:15 PM Re: disconnect for gate operator [Re: schenimann]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
They are usually 120v from my experience and I see no reason why a snap switch in a 3r box with a suitable cover would not work.
This is not really a motor load. It is just an AC/DC power supply that runs a DC motor and control system.
The ones I have worked on are fused at 10a on the 120v side.

Opening the battery back up as going to be another switch. You need something DC rated and 15a or so. There is usually a DC off inside the box tho.

It really depends on what they are trying to accomplish.
There is a lockout capability in most gate operators without doing all of this
_________________________
Greg Fretwell

Top
#206034 - 05/13/12 02:20 AM Re: disconnect for gate operator [Re: gfretwell]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
Greg,
Do you guys not have things like 5 pole SPST switches over there, the likes of the Kraus and Naimer CA-10 range, where if you need more contacts, you add another circular contact block on the back of the switch actuator?

Believe you me mate, these things have got me out of deep doo-doo before, most are rated at 500VAC/100VDC and you can get them in all sorts of switching configurations like SPDT, DPDT, you can have it as you like. wink
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#206036 - 05/13/12 08:36 AM Re: disconnect for gate operator [Re: schenimann]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
You might be able to find that switch but how do you get around the low voltage and line voltage in the same enclosure? You might be able to provide suitable barriers but you still have to convince the AHJ it s OK.
_________________________