The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 310 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#205941 - 04/29/12 07:59 PM Swimming pool water heater
MJ2000 Offline
Member

Registered: 06/29/05
Posts: 17
Loc: Toronto, ON
Does swimming pool water heater need to be protected with
GFCI breaker (50A)?
The heater(heat pump) is more than 10' from the pool.

Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#205951 - 04/30/12 07:43 PM Re: Swimming pool water heater [Re: MJ2000]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Mj.
In the States,the pool heater does not need to be GFCI. (2008- NEC) 680.9

680.26(6)(b). bonded and grounded per/instructions.

Top
#205952 - 04/30/12 08:54 PM Re: Swimming pool water heater [Re: MJ2000]
MJ2000 Offline
Member

Registered: 06/29/05
Posts: 17
Loc: Toronto, ON
Even if the code doesn't require a GFCI breaker, is it still worth the extra $100 for better protection?

Top
#205953 - 05/01/12 08:09 AM Re: Swimming pool water heater [Re: MJ2000]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
MJ:

IMHO, I would install GF protection. I don't have any CEC info for you.

An explanation of the benefits to the client, as opposed to the $$ for GF should help if the job costs are considered to be costly.
_________________________
John

Top
#205965 - 05/02/12 06:02 PM Re: Swimming pool water heater [Re: MJ2000]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Well the heater leaks current and a class A gfci won't even hold if the heater is large enough. Class b GF protection does not protect life so how can it work for life protection except that class b can be used where class a is not available? Actually look at rule 68-068 especially subrule 7
So if the heater is within 3 meters and not the other side of a wall then yes GFCI protection is required. If the heater is further than 3 meters then no.

Top