The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
09/30/16 04:48 AM
Temporarily feeding a panel...
by Potseal
09/29/16 11:05 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Potseal 7
Who's Online
2 registered (ghost307, cableguy619), 287 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#205909 - 04/23/12 12:16 PM Unequal tapping of a dual primary transformer.
LarryC Offline
Member

Registered: 07/05/04
Posts: 775
Loc: Winchester, NH, US
Question for you folks.

I have some dual primary / dual secondary transformers with a voltage tap on the primary windings. The primaries are wound for 120 V with a tap at 100 Volts. If I want to use them at full rated power and my supply voltage was 220 V, would I run into issues if I series the primaries with one wired for 120 V and other on wired for 100 Volts?

The units are AMVECO MT3750DS torroids.

Thanks.

Larry C

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#205910 - 04/23/12 12:49 PM Re: Unequal tapping of a dual primary transformer. [Re: LarryC]
geoff in UK Offline
Member

Registered: 12/30/02
Posts: 169
Loc: UK
I wouldn't forsee any problem with what you propose, provided the transformer is designed to give "full rated power" when used on the 100v taps.
Its just like having one primary tapped 100/120/220/240.