#205909 - 04/23/12 12:16 PM Unequal tapping of a dual primary transformer.
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
Question for you folks.

I have some dual primary / dual secondary transformers with a voltage tap on the primary windings. The primaries are wound for 120 V with a tap at 100 Volts. If I want to use them at full rated power and my supply voltage was 220 V, would I run into issues if I series the primaries with one wired for 120 V and other on wired for 100 Volts?

The units are AMVECO MT3750DS torroids.

Thanks.

Larry C
Top
Work Gear for Electricians and the Trades
#205910 - 04/23/12 12:49 PM Re: Unequal tapping of a dual primary transformer. [Re: LarryC]
geoff in UK Offline
Member
Registered: 12/30/02
Posts: 179
Loc: UK
I wouldn't forsee any problem with what you propose, provided the transformer is designed to give "full rated power" when used on the 100v taps.
Its just like having one primary tapped 100/120/220/240.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals