The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
52 minutes 53 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#205841 - 04/10/12 07:00 PM Emergency Circuit breaker panels
SJT Offline
Member

Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
Are any circuit breaker panels supposed to have a unique marking on them, to identify them from a normal power panel?
I'm talking in an industrial setting, where you have a lot of panels. The panel that is backed up with the generator, from a transfer switch.
Is it up to the electrician to identify them with a stripe on the panel? Any code rules (NEC,OSHA) about that?
Thanks - SJT

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#205844 - 04/10/12 08:29 PM Re: Emergency Circuit breaker panels [Re: SJT]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
Usual markings are determined by the engineer/design professional, and are part of the job 'spec'. That said, it varies by the scope of the job, the available power sources/voltages, etc.
The actual 'labels' are usually installed by the EC, along with the panel circuit directories.

As to 'code'; there are some requirements, ie: 'red leg' or ''high leg'; Fault current, Article 690 & 705, etc.

From the varied jobs I do plan review on, the PE/EE/Arch have panel ID spec'd out. A large data center has panel designations that would make your head spin!!

Scott35 may have some input on this.
_________________________
John

Top
#206421 - 07/01/12 08:55 AM Re: Emergency Circuit breaker panels [Re: SJT]
mikethebull Offline
Member

Registered: 03/18/07
Posts: 101
Loc: Rhode Island
700.10 (A) All boxes & enclosures (including transfer switches , generators & power panels) for emergency circuits shall be permanantly marked so they will be readily identified as a component of an emergengy circuit or system.


Edited by mikethebull (07/01/12 08:56 AM)

Top
#206428 - 07/01/12 05:51 PM Re: Emergency Circuit breaker panels [Re: SJT]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
Mikethebull:

Careful reading of the specific location of the genset, and WHY it is being installed has to be considered.

Article 700, 701 & 702 have to be reviewed, with 700 and 701 being the most stringent, as one is for Emergency systems, and 701 is for Legally Required Systems. 702 is commonly used for gensets at comm and industrial facilities for 'backup power'. Often, it is inadvertantly called "Emergency", but does not meet the requirements of 700.

The 'marking' for Optional are 702.7 (a)&(b).

A typical 'large' 702 genset may have two panels with chosen circuits, panels being marked 'Generator Panel'; 'Critical Circuit Panel', etc.

What things are labeled or called may or may not be what they are within the NEC definitions or intent.

700.2 from 2011 NEC:
Emergency Systems. Those systems legally required and
classed as emergency by municipal, state, federal, or other
codes, or by any governmental agency having jurisdiction.
These systems are intended to automatically supply illumination,
power, or both, to designated areas and equipment
in the event of failure of the normal supply or in the event
of accident to elements of a system intended to supply,
distribute, and control power and illumination essential for
safety to human life.
_________________________
John

Top